My war against dual rcd boards

As each (RCD) Residual Current Device must not have more than 30% leakage current on it.
It's hard to see how dual (RCD) Residual Current Device boards can be fitted at all these days.
i come across so many dual rcd boards with solar, evse and heat pumps on them, these have all been recently installed.
i wonder if BS7671 should state: Dual (RCD) Residual Current Device boards shall not be fitted, unless it can be shown (and documented) that they are suitable for the combined leakage currents expected .
otherwise developers will keep specifying them and i will have keep educating them on the many reasons a type A rcd should not be shared with other equipment!.
maybe manuafactuers instructions should also state : not suitable for a shared rcd, for certain equipment.
Parents
  • You’re right—dual‑RCD boards are increasingly fragile in modern installs (PV, EVSE, heat pumps) because standing protective‑conductor currents should be limited to ~30% of IΔn (i.e., ≤9 mA on a 30 mA RCD) to avoid unwanted tripping, per BS 7671 Reg. 531.3.2 guidance.

    The IET’s Wiring Matters (May 2021) shows typical leakage from today’s electronics accumulating across circuits—exactly the scenario that defeats shared RCDs on split‑load boards. Measuring and managing leakage at design/verification stages is advised. 

    For EV: BS 7671 Sec. 722 requires each EV point to be individually RCD‑protected (≤30 mA, all live conductors). Use Type A with 6 mA RDC‑DD or Type B if DC detection isn’t built in—another reason shared RCCBs are poor practice.

    For heat pumps/variable‑speed drives, consider Type F/B and upstream coordination to avoid DC blinding; mixing loads behind one Type A RCCB is risky. 

    Pragmatic recommendation:

    • Prefer RCBO‑every‑circuit or segregated boards for PV/EV/HP. Document measured standing leakage at design and handover. 
    • If a split‑load is unavoidable, demonstrate (and record) suitability against combined leakage and waveform types—your proposed BS 7671 wording aligns with current guidance and would curb developer “spec‑and‑forget” boards. 

    In short: don’t share Type A RCDs across modern power‑electronics unless you’ve proven leakage and compatibility; otherwise expect nuisance trips and reduced protection margin.

  • For EV: BS 7671 Sec. 722 requires each EV point to be individually RCD‑protected (≤30 mA, all live conductors).

    But consider the perhaps not unusual situation where the charge point has a 30mA RCD built-in (and likely a RDC-DD as well), but the soft skinned cable from the CU is concealed in a wall (so needs 30mA RCD protection to meet 522.6.202). Given the built-in RCD provides the individual protection, could the CU RCD, which is required only to protect the cable, not the EV, be shared? Ideally not perhaps, but in terms of meeting the actual requirements of the regs, as currently written?

       - Andy.

  • Does the EVSE meet BS EN 61008 (RCCB), BS EN 61009 (RCBO), BS 7288 (Socket Outlet RCD ?

Reply Children
  • Does the EVSE meet BS EN 61008 (RCCB), BS EN 61009 (RCBO), BS 7288 (Socket Outlet RCD ?

    For the sake of argument, let's say the RCD function does meet BS EN 61008.

    I know there was some debate about one particular brand a year or two back, where the manufacturer said it did while other distinguished observers begged to differ, so I'd hope that some manufacturers would have got their act together by now. Certainly I recall some early EVSEs simply incorporated ordinary DIN rail RCCBs or RCBOs - so some at least should have no doubts.

       - Andy. 

  • Ok if the EVSE has a approved/compliant RCBO at say 30mA then the upstream would probably need to use something like a 100mA or and S type/Delayed RCBO to avoid nuisance tripping issues.

  • then the upstream would probably need to use something like a 100mA or and S type/Delayed RCBO to avoid nuisance tripping issues.

    Nope, need to be 30mA non-delayed to provide additional protection for the concealed cable.

    There's no prohibition on daisy-chaining 30mA RCDs ... if fact it's mandatory in a few situations - e.g. caravan pitch socket and caravan incomer. The arrangement itself doesn't of itself introduce a risk nuisance tripping, merely the inconvenience of having to reset the other RCD  (or both RCDs) when a genuine fault occurs (provided all the other design parameters are correct).

       - Andy.