What is the economic argument? I doubt that margins are so fine on new-build developments that all-RCBO boards cannot be provided. With after-market solar PV installations costing £thousands, once again a few £tens more on a board change hardly matters
Try and compare a Hager (other brands are available) split load CU against a Navits CU
https://www.navitascp.co.uk/product-page/10-way-100a-mainswitch-consumer-units-c-w-t2-spd
The economic argument goes out of the window (other Apertures are available)
I see no reason why a fully RCBO and SPD type2 CU can not be designed and installed in the average UK dwelling
Sergio,
In my exeprience and despite what standards and regulations say, in majority of cases in domestic dwelling house work there is no "Designer". The installer or somebody may be signing paperwork as "Designer". But attitude is still very much "Its only a dwelling" what can go wrong?.
Cheers GTB
we don't yet have EV charging and solar PV.
So no heat pump RCD selection issues then
Or need that little bit extra clarity, particularly about the distinctions between requirements, regulations and specifications (there's a separate thread on that Requirement Structuring )
Not yet ...We won't have a heat-pump for many many years, certainly over 30 years from original CU installation.
... and even then (or if I'm wrong on the timescales) there's no reason a second CU can't be fitted for "renewable" technologies. The existing board doesn't have enough ways for EV, PV and HP anyway !
Don't get me wrong, I'm not saying it's a good idea to provide a dual RCD board for a brand new installation, or on refurb, but simply providing information that supports the fact there's no need to jump at removing these boards because they aren't compatible with new technology. Other options are available.
Can we assume they are type A RCD and not Type AC RCD
Can we assume there is also a Type 2 SPD and is fitted pre or post main switch
I have a 15 way dual RCD board on my home installation. I have lots of electronic equipment plus a full range of kitchen and laundary appliances, an outside workshop with machinary and a amatuer radio station. I have a standing earth leakage of 11mA acroos the 2 RCDs. Never had a nuisance trip other than the senior management pooring water over her steam iron, this got replaced with an early wedding present (she was lost for words and no dinner for me that night).
JP
Are the RCD type AC? The type AC could mask/blind the nuisance trip
Are the RCD type AC? The type AC could mask/blind the nuisance trip
That's an interesting point ... if, with the loads connected, the RCD is still able to operate within parameters from a Type AC RCD test (simulating a supplemental fault over the standing conditions), is that OK?
(I'm fully aware that what I'm proposing here is very "loose", but certainly a discussion point.)
However, we also need to consider that, in the "blinding" situations, currents, such as smooth DC, changing/pulsating DC, and/or high frequency AC, need to appear as a residual current ... and not all protective conductor currents, nor all 'leakage' currents are 'residual currents' in the live conductors.
And ... not all Type AC RCDs are 'blinded' in the same way, to the same thresholds.
The actual blinding from some electronic equipment might only occur during a fault downstream of some electronics - as shown in Fig A53.1.
And ... not all Type AC RCDs are 'blinded' in the same way, to the same thresholds.
Agreed
But we do know they (Type AC RCD) get blinded or may become blinded to a greater or less degree. Now consider the domestic dwelling for the scenario a light bulb fails (lamp to engineers) Home owner/occupier replaces it. Firstly the original lamp could of been filament or halogen or florescent/compact florescent the replacement surely by now will be LED thus the resistive load now becomes an electronic load with or without a certain amount of DC leakage.