Circuit breakers and rcbos.

 can different makes be put in different consumer units. Was at a job where the board was of a make that the wholesalers don't sell .as it happened the breaker start working

Parents
  • can different makes be put in different consumer units. Was at a job where the board was of a make that the wholesalers don't sell .as it happened the breaker start working

    Not really ... see Regulation 536.4.203 of BS 7671:2018+A2:2022.

    One of the main reasons for this is the conditional prospective fault current rating and associated UK-specific testing ... discussed further in this post: engx.theiet.org/.../153686

      gives very sound advice

Reply
  • can different makes be put in different consumer units. Was at a job where the board was of a make that the wholesalers don't sell .as it happened the breaker start working

    Not really ... see Regulation 536.4.203 of BS 7671:2018+A2:2022.

    One of the main reasons for this is the conditional prospective fault current rating and associated UK-specific testing ... discussed further in this post: engx.theiet.org/.../153686

      gives very sound advice