Main Earth Conductor Current (Bridge structure TN-C-S)

I have recently been tasked with carrying out some Inspection & Testing on a critical infrastructure graded bridge as part of a short term contracting position. 

I was sent out with the companies "Lead" electrician who is in the practice of making up paperwork/test results and trying to "look" busy whilst finding as much time as possible to dedicate to internet browsing. It put me in a bit of a pickle because I couldn't be a part of that when I'm part of the team responsible despite my signature not being asked for.

So I took the apprentice and decided to do some test & inspection. The particular job was a 3 yearly Inspection of the lighting and power circuits on the towers part of the bridge. There are three phase power circuits, three phase lighting circuits (phases split in the bridge but haven't yet found where) and single phase 110 volt sockets. 

The bridge is extensively metal. Every location where internal circuits are installed one is surrounded by box sections of steel bolted together.

The supply arrangement confirmed only by measurement (0.12 ohms) is TN-C-S fed from an adjacent 11KV transformer inside the bridge bowels sat on a concrete plinth in the basement. 

The inspection and testing has proven challenging due to scale, access and lack of prior adequate records  and I am still gathering evidence between juggling our other basic maintenance and reactive maintenance tasks. We were allotted 2 weeks to complete the lighting and power testing and had no schematics or location drawings to aid us everything has been visually verified and proven by testing. The area these circuits covers is huge and original installation between 1983 and 1985 with additions over the years. 

Wiring is almost entirely SWA, potentially some MICC left in the circuits.

Anyway that's the background. My concerns are as follows:

1. A reading as high as 730 mili amps - Taken with a clamp meter on the main earth supply from the HV/LV Transformer to MET. 

2. Suitability of a TN-C-S supply when surrounded by steel work and stood on a potentially great conductor. 

3. I have not been able to verify visually, or by test, the presence of main bonding conductors for the structural steel - This is due to the cable tray behind the main switch gear being inaccessible for visual inspection however I can see an unsheathed copper conductor, either 35mm or 50mm sq leaving the void. I have not worked out where the void enters the structure and require a long wander lead to carry out further investigation.

4. Due to limitations I had to test the final lighting circuit I.R at 250v with line & neutral connected together to earth. We have old 3c +N  PILC sub mains cables where the armouring is the CPC excellent I.R results > 700 Mega ohms some better than 999 Mega ohms. However on the PVC swa final lighting circuits we have readings as low as 0.4 megaohms and lots of them. Some are fine at 37-50 Mega ohms. The circuits are protected by BS88 10 amp fuses and have a mixture of LED and Fluorescent lighting.

5. There are a myriad of "end of line" points because the circuits have not been wired from point A-Z. Instead we have a main trunk in the towers with innumerous spurs off the main branch. Initially I was carrying out ZS readings (Live using insulated gloves) for convenience and to get a rough idea of Zs condition. However at some point I started to suspect the potential for parallel paths was almost certain given that many of the old fluorescent lights are metal clad, have bonding straps to the case from the cpc and are fixed to the steel by Unistrut fixings and similar providing earth continuity to the structural steel. 

6. I do not know if there is any continuity between the bridge structure and "true" earth, either by an intentional electrical conductor or by the natural design of the structure.

7. Reduced voltage readings were observed at several lighting junction boxes between 83 and 153 volts. No labelling and no way to determine circuit and phase. 415 is present in some JB's

8. Multicore swa cables some with 8 conductors, have not been identified in anyway. I am most concerned that neutral and cpc's have been mixed and the bridge is forming a neutral.

This inspection has me wanting to pull the main fuses and hand it to the client in a sealed skull and cross bone bag. If I were to go off coding, individually there are no C1 faults. But as a whole, without other records, design data and further verification I have reasons to suspect it could be extremely unsafe and due to the age, vibration and hot cold fluctuations if a fault does occur, at this stage I cannot say how risky it is.

I have all my guidance notes here and am preparing a customised report with photographs, test results etc. 

I am seriously concerned with the possibility of the PEN conductor being lost, and where would that 700 or so miliamps flow to? I have no reference earth to use.

My main recommendation is that the bridge requires a robust bonding system, and a back up TT earth system which is tested regularly due to general public pathway on the bridge (Being metal) contractors and employee's traversing the internal bare metal structure daily.

I would really appreciate your thoughts 

Parents
  • I am seriously concerned with the possibility of the PEN conductor being lost,

    I think the plethora of dire warnings about loss of PEN in EVSE installations have driven a sense of unnecessary paranoia about the subject in other situations. I concur that it would be the duty of an inspector to consider each on its own merits, but from a general perspective 114.1 offers the fundamental consideration that where ESQCR applies, the connection of the supply neutral with earth can be regarded as permanent. As I read it, that means the integrity of the supply neutral can be considered fully in place.

    It begs the question why it was thought necessary to flap about loss of PEN at all, but there you go! Maybe dire consequences were envisaged for EV charging should the DNO fail in their duty to prevent loss of neutral and thus huge expense was incurred in the implementation of measures to mitigate the risk, hence the requirements of 722.411.4.1. If there really was serious concern, then you would imagine that the absence of those control measures would also have been serious. Clearly, there are some who think it is only worthy of a recommendation.

     Best Practice Guide 4 version 7.2 gives the absence a Code 3.

    ( I would have posted the actual statement but it looks like the bods have been messing around with things and I can no longer use my snipping tool to post). 

     

  • It begs the question why it was thought necessary to flap about loss of PEN at all

    It's not new to EVs - similar concerns have been there for PME with caravans and boats for a very long time (probably predating the ESQCR). Whereas other metalwork outdoors (e.g. street lights) have been happily on PME with nothing more than the occasional additional electrode thrown in. I suspect much of the apparent inconsistency comes for the wider situation rather than the electrical installation per se - i.e. how likely are wet/bare feet. how often will someone actually grab hold of the thing, is the ground likely to be covered with vaguely insulating tarmac and so on.

    the connection of the supply neutral with earth can be regarded as permanent

    All depends on your definition of "permanent" - I suspect the dictionary has it closer to "indefinitely" rather than "forever" - i.e. it could well come to an end someday, we just don't know when yet.

       - Andy.

Reply
  • It begs the question why it was thought necessary to flap about loss of PEN at all

    It's not new to EVs - similar concerns have been there for PME with caravans and boats for a very long time (probably predating the ESQCR). Whereas other metalwork outdoors (e.g. street lights) have been happily on PME with nothing more than the occasional additional electrode thrown in. I suspect much of the apparent inconsistency comes for the wider situation rather than the electrical installation per se - i.e. how likely are wet/bare feet. how often will someone actually grab hold of the thing, is the ground likely to be covered with vaguely insulating tarmac and so on.

    the connection of the supply neutral with earth can be regarded as permanent

    All depends on your definition of "permanent" - I suspect the dictionary has it closer to "indefinitely" rather than "forever" - i.e. it could well come to an end someday, we just don't know when yet.

       - Andy.

Children
  • All depends on your definition of "permanent" - I suspect the dictionary has it closer to "indefinitely" rather than "forever" - i.e. it could well come to an end someday, we just don't know when yet.

    A bit like the Universe perhaps! 

    I think the issue of open PEN has been well and truly covered on the forum, whether EV, caravan, boats, PFS. Refreshing to now include steel bridges! 
    I was merely pointing out that if the DNO provides a PEN suitable for the installation to connect its exposed and extraneous conductive parts to, why would there be any need to question its integrity?