48V DC Telecoms Equipment Disconnection Time

Is the disconnection time for 48V DC Telecoms Equipment supplied from a rectifier 5 seconds?

I have also seen 0.3s & 0.8s mentioned which is throwing me a little.

Where is this listed in BS7671, is it 411.8 as this doesn't specify DC?

Parents
  • Traditional 'plain old telephone system or POTS' 48V wiring does not really have a disconnection time, as the system is current limited, and a shorted line can be supported for ever (in fact current flow is how the exchange knows the phone is 'off hook' ) 

    There are a great many telecom related things (power over ethernet comes to mind as a modern one) that have continued this current limited rather than ADS safety philosophy. 

    There is no shock hazard disconnection requirement in BS76771 that sets a rapid disconnection time for voltages that are below LV, and count as ELV 50V AC / 120V DC. 

    There are however other standards that will apply, such as the BT SINs and various IEEE standards and of course any maker's instructions.

    What is the system you are considering supplying ?

    Mike.

Reply
  • Traditional 'plain old telephone system or POTS' 48V wiring does not really have a disconnection time, as the system is current limited, and a shorted line can be supported for ever (in fact current flow is how the exchange knows the phone is 'off hook' ) 

    There are a great many telecom related things (power over ethernet comes to mind as a modern one) that have continued this current limited rather than ADS safety philosophy. 

    There is no shock hazard disconnection requirement in BS76771 that sets a rapid disconnection time for voltages that are below LV, and count as ELV 50V AC / 120V DC. 

    There are however other standards that will apply, such as the BT SINs and various IEEE standards and of course any maker's instructions.

    What is the system you are considering supplying ?

    Mike.