Is the disconnection time for 48V DC Telecoms Equipment supplied from a rectifier 5 seconds?
I have also seen 0.3s & 0.8s mentioned which is throwing me a little.
Where is this listed in BS7671, is it 411.8 as this doesn't specify DC?
Is the disconnection time for 48V DC Telecoms Equipment supplied from a rectifier 5 seconds?
I have also seen 0.3s & 0.8s mentioned which is throwing me a little.
Where is this listed in BS7671, is it 411.8 as this doesn't specify DC?
Where is this listed in BS7671, is it 411.8 as this doesn't specify DC?
48V d.c. isn't RLV, but ELV. Disconnection times for ADS are per table 41.1 - which for ≤120V d.c. says no disconnection needed for protection against shock. (Basically ≤120V d.c. is treated pretty much live ≤50V a.c. - i.e. in normal dry conditions is considered safe to touch).
You probably still need to protect conductors (or rather their insulation) from physical damage in the case of shorts and overloads - but the timing of that is much more open (5s is often used as a maximum for dead shorts, just to simplify the calculations, as things are mostly still adiabatic in that range).
- Andy.
Where is this listed in BS7671, is it 411.8 as this doesn't specify DC?
48V d.c. isn't RLV, but ELV. Disconnection times for ADS are per table 41.1 - which for ≤120V d.c. says no disconnection needed for protection against shock. (Basically ≤120V d.c. is treated pretty much live ≤50V a.c. - i.e. in normal dry conditions is considered safe to touch).
You probably still need to protect conductors (or rather their insulation) from physical damage in the case of shorts and overloads - but the timing of that is much more open (5s is often used as a maximum for dead shorts, just to simplify the calculations, as things are mostly still adiabatic in that range).
- Andy.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site