Disconnecting conductors for testing

We have a contractor in the training centre at the moment. He is dressing conductors and re-terminating connections in several distribution boards on our testing rigs. Frequent dismantling has caused a birds nest of what was just a short while ago, neatly dressed boards. Loose connections, damaged conductors ends and mcb terminals. 
Not unexpected but it does indicate that there is disadvantage in too much disconnection and re-connection. Doing so a few times during the life on an installation might be ok but do we really need to? Sure, some test procedures do require dismantling but for certain procedures such as R1+R2 continuity tests might it not be reasonable to accept the technical constraints and simply leave conductors connected.

I note GN3 shows the cpc remaining in the earth bar but with the line disconnected. The test App promoted for candidates preparing for AM2 shows both line and cpc disconnected. The problem is that often these publications are treated as sacrosanct by those setting assessments. Deferring could be costly for a candidate. 

Parents
  • I did a domestic EICR today where the CU was changed in 2023. Pretty much every cable in there had been extended with crimps that were tucked nicely in the back. There was no way I was going to disconnect or disturb any of the cables in there and risk loosening one of them.  Thankfully IR was satisfactory.  I just checked all screws for tightness checked the RCBO's and main switch operated correctly then put a link over to the RCBO live to do my r1+r2 readings without removing the cables. I did ring continuity at the sockets. 

    Gary

Reply
  • I did a domestic EICR today where the CU was changed in 2023. Pretty much every cable in there had been extended with crimps that were tucked nicely in the back. There was no way I was going to disconnect or disturb any of the cables in there and risk loosening one of them.  Thankfully IR was satisfactory.  I just checked all screws for tightness checked the RCBO's and main switch operated correctly then put a link over to the RCBO live to do my r1+r2 readings without removing the cables. I did ring continuity at the sockets. 

    Gary