Current transformers
In distribution subs they have thermal ammeters I think they have a 30 minute warm up time so they don't get hammered by large starting currents or faults. I think I'm right in saying that the meters are switched out if circuit forr most of the time I'm you'd you can't leave CTs open circuited so do they just put a resistor across  the CTs in are the meters usually left in circuit.
  • the insulation from the meter tails is not the problem,
    No, it's the insulation and protection of the conductors from the current transformer, and of the current transformer itself, because of the voltages created. We no longer have 'limitation of discharge of energy', and there are good reasons for that.
    These conductors are not SELV ... so they must be FELV or LV ... and you see where this goes from here in BS 7671 terms.
  • Also a lot of "consumer" CTs have either a burden resistor or voltage-clamping (e.g. back to back zeners) built-in.
    I'm not 100 % sure this is the case ... and if it is, what if those devices fail? 'Guaranteed SELV' CTs are very expensive!
  • One example: https://www.makerhero.com/img/files/download/SCT013-Datasheet.pdf
    Failure of the voltage clamping must be possible of course.It would have to be part of a chain of failures to become hazardous though - e.g. circuit broken circuit plus failed basic insulation, or being dismantled/disconnected without taking the basic precaution of unclipping it from the meter tails as well as the monitored circuit carrying a significant current at the moment concerned - combined with the chances of the voltage clamping itself failing. So maybe not drastically more dangerous than say ADS where the simple failure of a c.p.c. can entirely remove protection.
    The high voltage is associated with an infinite impedance of an open circuit though - to get a shock presumably a body resistance (in the region of 1kΩ?) would have to be in-circuit and therefore limit the voltage (and current) available to some extent?
  • Failure of the voltage clamping must be possible of course.It would have to be part of a chain of failures to become hazardous though - e.g. circuit broken circuit plus failed basic insulation,
    The device you linked to has an audio jack on it, so only one fault (failed resistor) is necessary.
    However, that is also based on the assumption that the burden resistor type is selected. The 1 V output is pretty non-standard for a monitoring interface in a building, because there could well be a problem with EMC if there's a long-lead connection in an installation.
    I've certainly seen a lot that are a basic current transformer, no built-in burden resistor, with simple insulation on the leads for connection - these only need a single fault (open-circuit conductor) to be a hazard.
  • Unfortunately, that ship is already passing through the harbour entrance and heading out into the world.  Consumer CTs intended to clip round meter tails with whatever protection their suppliers deem appropriate have been out there for over 20 years (at least since the first home energy monitors appeared in the 1990s) and the fitment rate is taking off rapidly with the proliferation of EVSE and PV.  Some of them make a nice buzzing sound if clipped round a tail without being connected - I'm not sure whether that is internal arcing or the operation of a protective device and haven't had the time to investigate.
    Ideally we would have rolled out a simple standard interface giving basic electrical data (voltage, current, power, etc.) as part of the smart meter roll-out, completely avoiding the need for clip on CTs (a great application for cheap plastic fibre optics, since only uni-directional communication over relatively short distances is required).
    (I also note that smart meters are probably the logical place for things such as a standardised approach to G100 style CLSs (especially in a domestic setting and if multiple manufacturers devices need to work together) and possibly even open PME neutral detection, but maybe I'm getting a little controversial now...).
  • Ideally we would have rolled out a simple standard interface giving basic electrical data (voltage, current, power, etc.) as part of the smart meter roll-out, completely avoiding the need for clip on CTs (a great application for cheap plastic fibre optics, since only uni-directional communication over relatively short distances is required).
    For energy management, it's important to be able to look at import and export current as well as voltage.
    There are alternative approaches, where an energy monitoring unit (that has CTs and VTs built in) connects in-line with the tails, and communicates via CANbus/Modus back to the energy management system (e.g. inverter).
    Agreed ... it's those I'm talking about, not all are installed correctly (and as discussed above, perhaps some are not installed in accordance with BS 7671).
  • The device you linked to has an audio jack on it, so only one fault (failed resistor) is necessary.
    Fair point. Of course wire-ended versions are available too. Interestingly Victron seem to have switched from plugs to hard-wired in their recent models - they might have had similar thoughts.
  • as part of the smart meter roll-out, completely avoiding the need for clip on CTs
    Except that sometimes what's meant to be measured doesn't necessarily pass completely and individually through the supplier's meter - e.g. total generation for PV or consumption for specific load (heat pump or EV). Mind you extending the smart meter system to PV generation meters might not have been a bad idea...
    That's very close to what the French did, their 'Linky' smart meter, used for the French smart meter roll-out has a transmit-only serial interface, TIC (Tele-Information Client), albeit wired rather than fibre optic, providing the various meter measurements along with a range of smart control signals that can be used to automate different loads, for switching things like EV chargers, space heating, water heating inline with time of use tariffs. The meter measurements can be used by smart EV charge points to dynamically adjust the charging rate, to avoid overloading the incoming supply.
    Further, the French make the TIC interface available to the end consumer, so when the electrician is installing new loads, like an EV charge point they can connect up the TIC comms to the charge-point as part of the installation, so it is controllable and can work with TOU tariffs from day 1.
    I take my hat off to the French engineers that designed it, it's a very well thought through, logical solution to the problem. As for the British smart metering system.....
  • Except that sometimes what's meant to be measured doesn't necessarily pass completely and individually through the supplier's meter - e.g. total generation for PV or consumption for specific load (heat pump or EV). Mind you extending the smart meter system to PV generation meters might not have been a bad idea...
    And not all supplier's meters are 'bidirectional', i.e. don't measure 'export' (or 'feed-in', 'reverse feed' or whatever term is in vogue).
    I understand SMETS2 and later are supposed to though, so it's coming.
    But yes, load control and some energy management system functions need to know what current is on certain circuits, or groups of circuits, rather than the whole installation.