Hi Guys
I installed a sub-main today to a domestic garage. Earthing is TT. Ra is 137ohms. Existing house CU has a front end S type RCD. I have run the sub-main from the S type side of the split load board. I have an r1 + r2 of 0.36 ohms to the garage. When I tested Zdb at the new garage board I have just fitted I am getting a reading of 318 ohms. (garage is attached to house for what it's worth). After a bit of investigation It looks like I am getting this massive uplift through the time delayed RCD. Is there likely to be an issue with the time delay RCD or is this normal. Ordinarily 318ohms would not be acceptable as it could indicate the spike being unstable but that is not the case here. I obviously have 30m/a protection for the outgoing circuits at the garage.
Gary