For a standard domestic Install, split board with 2x Type AC main switches.
No PV or Car Chargers should this be a C3 or C2?
Thanks in advance
For a standard domestic Install, split board with 2x Type AC main switches.
No PV or Car Chargers should this be a C3 or C2?
Thanks in advance
Then again, if you follow the advice given in Appendix 6 7671 with respect to producing an EICR, you should only record issues that could give rise to danger. That is another fuzzy example of wording in 7671. My take is that something that "may give rise to danger" is something that could be potentially dangerous, which a code 3 is definitely not.

Then again, if you follow the advice given in Appendix 6 7671 with respect to producing an EICR, you should only record issues that could give rise to danger. That is another fuzzy example of wording in 7671. My take is that something that "may give rise to danger" is something that could be potentially dangerous, which a code 3 is definitely not.