For a standard domestic Install, split board with 2x Type AC main switches.
No PV or Car Chargers should this be a C3 or C2?
Thanks in advance
For a standard domestic Install, split board with 2x Type AC main switches.
No PV or Car Chargers should this be a C3 or C2?
Thanks in advance
Nearly two weeks of discussion and nobody has mentioned high-frequency currents.

Be sure to read the complete article .. "ordinary" B-types aren't good enough for Vaillant (and perhaps other brands as well) - you need a special B-HP type (which are even less affordable than a B-type) - presuming you need 30mA RCD protection on that circuit in the first place that is.
nobody has mentioned high-frequency currents.
Sergio did mention B and F types 9 days ago ... but easily missed in the Forum's non-linear, not-quite-tree structure :-(
- Andy.
Be sure to read the complete article .. "ordinary" B-types aren't good enough for Vaillant (and perhaps other brands as well) - you need a special B-HP type (which are even less affordable than a B-type) - presuming you need 30mA RCD protection on that circuit in the first place that is.
nobody has mentioned high-frequency currents.
Sergio did mention B and F types 9 days ago ... but easily missed in the Forum's non-linear, not-quite-tree structure :-(
- Andy.