Do I need to run bonding conductors from each meter?

Hi,

In a block of 18 flats, each flat has its own 1ph electric supply and a copper water supply stop-cock and copper gas stop-cock all bonded together after the stop-cocks as they enter the flat, with a current NICEIC periodic certificate.

My question is: 

As the gas meters for all the flats are in a cupboard outside on the ground floor, they are bonded with the water supply to the landlord's supply and have a current niceic periodic certificate for the common parts

I have been informed that we now need to run bonding conductors from each meter to each individual flat, is this correct?

David

Parents
  • I have been informed that we now need to run bonding conductors from each meter to each individual flat, is this correct?

    I'm not sure I'm picturing this correctly - if you're saying the gas/water services where the enter they building are all bonded to the incoming supply earth terminal, and within the flats, which have a protective (earth) conductor run along with the L&N from the supply - the water/gas are bonded to the pipework near the point of entry to the flat to the flat's earth terminal- then all sounds well to me.

    (If on the other hand the suggestion is that the flat's earthing is relying on the water/gas pipes, then there a bigger problems...)

    If some-one told you the bond need to be with 600mm of a meter and so a cable needs running out to an external meter, they're only read half the regulation - that only applies where the meter is internal (e.g. to the flat, where the installation belongs to the flat).

       - Andy.

  • I'm not sure I'm picturing this correctly

    Nor I, but it seems that the gas and water are bonded to the electricity supply adjacent to where they enter the building.

    If I understand correctly, the gas and water are also bonded to the electricity intake within each flat.

    I cannot see the need for any further main bonding.

Reply
  • I'm not sure I'm picturing this correctly

    Nor I, but it seems that the gas and water are bonded to the electricity supply adjacent to where they enter the building.

    If I understand correctly, the gas and water are also bonded to the electricity intake within each flat.

    I cannot see the need for any further main bonding.