I am currently commenting on a Pre-Fabricated Bathroom Pod design where the designer is specifying a junction box for final connection & testing of the pod with the pod being wired in LSZH Tw & E cable. Slack should be left on cables so that the junction box can be dropped through an access hatch for connection purposes with future access to the junction box post completion for testing and inspection.
I reject this design on the basis that Tw & E cabling is 'fixed wiring' and that in accordance with BS 7671 521.9.2 wiring should be undertaken using heavy duty flexible cables H07ZZ-F LSZH Flexible Mains and Control Cable - 1mm² to 630mm² in lieu of Tw & E, however the bathroom pod designer and the clients MEPH Technical Project Engineer are arguing against such wiring.
Can someone advise who is right or wrong.