Insulation and thermal bridging and an EV charger

The situation is a garage being converted into a TV room

External wall with batten attached which is to be insulated with 75mm PIR insulation and plaster boarded
Stud is only 70mm!!

Picture attached...

The house CU is high up on the wall. the tails ran down the internal garage wall to the outside meter box
A second CU was mid way down the wall feeding  an external EV charger, the tails of which also went to the external meter box

The tails were in plastic conduit surface mounded.

Since the tails (no RCD protection)to both boards are to be hidden by the plasterboard, I though best to put in two lengths of earthed metal conduit (50x50)
The 10mm feed to the 7kW charger is clipped to the batten.

The owner is doing the batten and insulation.
I am concerned about insulation being near my cables and trunking


I presume the trunking it self will be a break in the insulation so could be a thermal bridge?

Could you run the insulation up to the trunking or should they be a gap.

cables clipped along the batten how far should they be from the insulation,
I would like to leave about a 50mm gap? but this will cause this thermal bridge issue I believe?

Also say if  a 2.5mm  socket radial (fused to 16A) was ran through the batten and against the concrete block 
with insulation over it. What installation method would you consider that. I presume these soft concrete blocks have some insulation factor.
Will they be much of a heat sink?

I am concerned about the EV cable really as a continuous load in this stud work. Its has a bit of extra capacity as 10mm2 for a 7kW charger.

How can the wall be adequately insulated, without bridging and the cables be safe?

Thanks

  • In the original drawing in the first post there are 2 cross sections, one with the insulation between the battens and one with it on the surface of the battens. If the owner does the second, a lot of the problems disappear.

    Couple of things spring to mind, if the tv is wall mounted there might need to be studs inset into the insulation for support. And if the CUs are metal, and presumably not brought forward to the new surface, they could suffer from increased condensation as they will be colder than the air in the new room

  • Thank you.

    Can quite visualise you plan Andy

    I'd probably run the tails on the surface in PVC trunking inside then dive through the insulated wall for the shortest distance to the meter box.

    On the surface of what ? please

    The owner is thinking of not insulating the section with the tails, but that could be an issue?

    Ive attached another pic.

    The tails and main board do not line up
    The main boards tails are outside of any zones.




  • Sorry I won't keep on, one last thought on this.
    In the stud bay with the meter tails
    On the block wall install 20mm layer of  PIR type insulation
    Mount the metal trunking onto this or a thin ply layer if better
    Then plaster board over
    Ca ble not in insulation
    Good free air coverage
    plasterboard will enable heat dissipation
    thermal bridge reduced

    ?

  • On the surface of what ? please

    Interior surface - i.e. on top of the plasterboard. That way they're not concealed so all the issues zones or concentric earth protection, not to mention being embedded in thermal insulation all go away (apart for the short distance through the wall to the meter box). If the customer is happy with two CUs surface mounted on that wall, a bit of extra trunking shouldn't be too hard a sell.

    The owner is thinking of not insulating the section with the tails, but that could be an issue?

    It's pretty rubbish from a thermal point of view - with risks of condensation both on the plasterboard surface and against the original wall (risking rot of the studs - the pictures seem to suggest untreated timer is being used too Rolling eyes)

       - Andy.

  • Table 4A2 should help, but for me, it seldom shows exactly what I want.

    The difference between numbers 2 and 60 seems to be largely the degree of insulation around the conduit. I find it difficult to believe that there would be any significant difference between round conduit and rectangular (or square) ducting.

    No. 2 has the conduit touching the inner skin, but yours touches the outer skin, which will be cooler.

    Page 431, RM A: "Heat from the cables is assumed to escape through the inner skin only."

    RM B: "Were the conduit is fixed to a masonry wall the current-carrying capacity of the ... cable may be higher."

    Your ducting is attached to the cool outer surface of the void.

    What is the probability of the main tails carrying 80+ A for an extended period?

    You have to choose between RM A and RM B. I think that if the bay between the studs is filled with Rockwool (or similar), you will not go far wrong.

  • Thank you Chris.
    Just to clarify a few thing I may be misunderstanding
    Is this with your earlier comment on the installation method that would require the service fuse to be  derated to 80A ( if its actually s  a 100A fuse) for this solution

    Agreed, so now the DNO's fuse needs to be downgraded to suit.

    I think that if the bay between the studs is filled with Rockwool (or similar), you will not go far wrong.

    Do you mean put rock wool in the bays either side of the section with the tails in,
    or put rock wool in the bay with the tails in (to limit thermal bridge issues)

    Many

  • Is this with your earlier comment on the installation method that would require the service fuse to be  derated to 80A ( if its actually s  a 100A fuse) for this solution

    Yes, if you choose RM A.

    put rock wool in the bay with the tails in (to limit thermal bridge issues)

    Yes.

    you will not go far wrong

    Sorry, I should have added, "with RM B".

    Please note that I am no expert at all on insulation and where you put you permeable and impermeable barriers, etc.

    Sometimes, if you go by the letter of all of the building regulations, etc., the customer just cannot have what he (or she) wants. So, compromises are necessary and you do the best that you can.

  • and, if it is more than 50mm below the celotex, cable is out of zones anyway. 

    It would be better in terms of cable rating if the tails could use the blockwork as heatsinking. It is probably not so good from a room thermal and condensation damage perspective.

    Mike. 

  • I presume these soft concrete blocks have some insulation factor.
    Will they be much of a heat sink?

    Presuming we're talking aerated concrete blocks here (e.g. thermalite or celcon) - the ones that usually have squiggles on their surfaces and look like an aero bar when broken - then yes they have a bit of insulating property - although not a huge amount.  Lambda values (W/mK) are around 0.15 - which compares with timber, conventional concrete blocks are closer to 1.1 (so about 7x as thermally conductive) whereas "proper" thermal insulation is more like 0.033 (wooly stuff) or 0.022 (PIR/PUR board - kiindspan or celotex) (so about 1/7th as thermally conductive as aerated blocks).

      - Andy.

  • Would it not have been simpler to have lowered DB2 to the same height as the meter box as all the cables from it appear to go down anyway. Just put it behind some furniture flushed in.

    Gary