Within BS7671 there is a lot of information in the use of RCBOs and was wondering if in certain applications like industrial sockets BS90437 and lighting Circuits whether these would pose a nuisance tripping action.Just wondering what the general consensus

When using high current needs equipment like machinery (ie Milling Machinery and Lathes) would the use of RCBOs pose an inderence with constant tripping as with lighting applications could even leave you without lighting. Just wondering the general consensus? 

Parents
  • BS60439-3

    That's the old standard for DBs isn't it? (replaced by BS EN 61439-3 about 10 years ago?)

    As for RCBOs BS 7671 has no blanket requirement - 30mA RCDs are only demanded for additional protection on lighting circuits in domestic/household situations. Normally no requirement for hard-wired equipment, just sockets (<=32A) used by ordinary persons and for portable equipment outdoors. Soft sheathed cables concealed in walls normally aren't a feature of industrial situations.

    Most single appliances suitable for being powered by a plug have relatively low earth leakage (protective conductor) currents - otherwise you'd have other constraints, such as having to provide high integrity c.p.c.s. It can be an issue in some situations though - e.g. server racks containing dozens of mains powered items but the whole thing still on a plug & socket for maintenance purposes. In such cases there is an option to use a risk assessment to avoid the need for 30mA RCD additional protection.

    Sometimes high starting currents have been know to false trip RCDs - usually the answer to that is to use an RCCB with a higher carrying current rating (e.g. a 40A/30mA RCCB plus say a 16A MCB, rather than a 16A/30mA RCBO).

       - Andy.

  • Hi Andy,

    Yeah, I've got my standards wrong it should of been BS60947-3 its the Industrial standards and not 90437 which I gave first time round. 