Metering enclosures - is plastic OK?

We have a bit of our business that installs additional submetering into non-domestic premises.  This typically involves fitting CTs to sub-main/distribution circuit cables and connecting those to a meter in a DIN rail enclosure that we provide.  There will be an associated supply for the meters, usually as a dedicated final circuit from a local distribution board with the circuit protection fitted in that board.

We use plastic DIN rail enclosures generally, as we do not regard these as 'switchgear'.

We had a challenge on one project (in a hospital) where the client (after installation) declared these to be switchgear and non-compliant with the regulations as they were not metal.  All arguments relating to definitions to BS7671 fell on deaf ears, and the hospital-specific guidance which he cited made no mention of such a requirement.  Pointing this out was similarly futile.  

Eventually we replaced them for metal enclosures - and charged the customer for the replacement.

It got me wondering though - is there anything from a regulatory perspective that would mandate use of steel enclosures for (just) metering?  Would that change if there was an MCB/RCBO in the same box providing protection for the meter (s)(and nothing else)?

Thanks,

Jason.

Parents
  • As far as BS 7671 is concerned the "non-combisible material" for consumer units and similar switchgear assemblies (421.201) only directly applies to domestic (household) premises.

      - Andy.

Reply
  • As far as BS 7671 is concerned the "non-combisible material" for consumer units and similar switchgear assemblies (421.201) only directly applies to domestic (household) premises.

      - Andy.

Children
  • As far as BS 7671 is concerned the "non-combisible material" for consumer units and similar switchgear assemblies (421.201) only directly applies to domestic (household) premises.

      - Andy.

    Agreed, but it is not unreasonable to extrapolate that there must be a general concern about fire propagation when plastic enclosures are used. Where there is a sleeping risk or a significant difficulty in evacuating a building, it might be reasonable for a fire risk assessment to acknowledge the concern and require mitigation.