Bonding of incoming services

Hello all,

I have carried out a fire risk assessment and noticed that, although there is no gas meter or installation, the metallic gas service entering the building and continuing for approximately 800mm is not bonded, although there is an earth bond coiled up next to it. 

I'm in two minds whether to recommend it be connected, or if this would introduce further potential hazards. 

It can be touched, particularly while turning electricity supplies on and off, but not likely during the general occupation of the building. 

Any thoughts?

Parents
  • I dont really think it is practical to box it in and expect it not to be obstructed or the vents covered. It probably is plastic outside, the building is 1980s construction. 

    I think for what it is, I'll recommend it be bonded and if gas is provisioned then reconfigure the bonding to suit

    Thanks 

  • The pipe does not belong to the owner or operator of the premises ... do you have permission of the owner of the pipe (gas distributor) to make that connection?

    I'm guessing this fact is why it's left as-is ...

Reply
  • The pipe does not belong to the owner or operator of the premises ... do you have permission of the owner of the pipe (gas distributor) to make that connection?

    I'm guessing this fact is why it's left as-is ...