Phase and neutral cables entering a metal enclosure through separate holes

I have come across an Installation with the supply single AWA cables glanded off into a aluminium plate. Its a 800A  installation with three phase and neutral cables all passing through separate holes so Eddy currents are a concern.

Anybody got any views ? 

Parents
  • If they all come in through the same non-magnetic plate, then there is no risk at all of magnetic heating as there may be with a steel plate close to the current cores,  But if the armours are in effect all linked metallically at both ends then there will be current in the armour loop - like  one turn transformer with a very large air core. If there is no evidence of heating of the plates or glands, then there is nothing to worry about.  In that sense providing the thickness of the plate and the tightness of the glands is good enough for the current loop there is no issue. 

Reply
  • If they all come in through the same non-magnetic plate, then there is no risk at all of magnetic heating as there may be with a steel plate close to the current cores,  But if the armours are in effect all linked metallically at both ends then there will be current in the armour loop - like  one turn transformer with a very large air core. If there is no evidence of heating of the plates or glands, then there is nothing to worry about.  In that sense providing the thickness of the plate and the tightness of the glands is good enough for the current loop there is no issue. 