Soil thermal resistivity and ambient temperature

For buried cables, the soil thermal resistivity and ground ambient temperature are required to be able to calculate the CCC of the buried cable.

The Regs states 2.5 K.m/W and 20 °C respectively but with the caveat that other values may be used either where measured or the ERA figures can be used.

Table 4A2 shows example drawings of buried cable which appear to show the cable buried direct in the soil with no indication of sand/pea gravel bedding, cover etc. (How many installations just dig a trench, drop the cable in then just backfill with the soil that's been dug out with no bedding/cover?)

Chapter 16 of the Commentary on the Regs states that the 2.5 K.m/W value is "conservative" and that "...BS 7769-3-1 (IEC 60287-3-2) provides standard conditions for the UK as follows:" and lists 1.2 K.m/W and 15 °C.

1. Why doesn't the Regs use the "standard conditions for the UK"?

2. Where does sand/pea gravel bedding/cover come into this, or is the "conservative" 2.5 K.m/W meant to cover such but it just isn't mentioned anywhere?

Parents
  • (How many installations just dig a trench, drop the cable in then just backfill with the soil that's been dug out with no bedding/cover?)

    I would have thought quite a lot - especially at the domestic end of the market. As long as the soil doesn't contain sharp stones and isn't going to be compressed significantly, it usually works out fine (obviously quite different in flinty soil under a roadway).

    Where does sand/pea gravel bedding/cover come into this

    There does seem to be a tendency to ignore such things - e.g. indoors adding capping or putting a cable into a conduit seems not to require a change in reference method - and until not so long ago, an underground cable could be buried direct, or in ducting, for the same reference method. So my guess is that the standard figures do make an adequate allowance for usual sorts of air gaps immediately surrounding the cable.

       - Andy.

  • Yeah, I suppose I'm thinking more of the industrial end whereby I'd expect bedding/cover etc.

  • For all the installation methods, dont forget that the figures in the big book are informative annexes, not normative rules you must follow, so if you have more accurate data for the specific cable or installation conditions or loading profile, you are always welcome to use that information. This may allow one  to deduce a less wasteful cable size, and on big projects where it is worthwhile it is done.  But equally, for short runs and JFDI jobs where something just has to be done right now and work first time, and the cable price is not dominant, the effort to perform and document the accurate calcs, and to be confident to do so, is not really worth it, and the one size fits all approach is more sense. 

  • Thumbsup