Diversity settings for apartment blocks and ADMD standard norms

I'm looking at calculating a total diversified load for a small apartment block. Using Table A2 in the OSG i am able to get the majority of the diversity settings however does anyone know of any standard norms when it comes to diversity considering the amount of apartments. Say for example the total diversified load per apartment is 50A and there is 8 apartments. Technically you would need a 400A capable supply to feed these apartments however this doesn't take into account that not all apartments will be drawing their maximum load at any one time.

I have come across a french standard  NFC14-100 which gives correction factors depending on the amount of apartments you have. Estimation of actual maximum kVA demand - Electrical Installation Guide

Does anyone know of anything similar in British standards or standard norms used by the DNO for this?

Parents
  • The traditional 2KW per dwelling (see the graph in the post by mapj1) assumes gas central heating.

    If these new apartments all have heat pumps and car chargers, then you need to allow for that. 

Reply
  • The traditional 2KW per dwelling (see the graph in the post by mapj1) assumes gas central heating.

    If these new apartments all have heat pumps and car chargers, then you need to allow for that. 