Correct EICR coding for a socket supplying a Server.

What should the code be for a Socket circuit supplying a Data Cabinet/Server up to 32a that has no 30mA RCD protection? 

  • a single 'off earth' fault does not make anything immediately dangerous

    Now we're getting into 543.7 territory ... which isn't as robust as it used to be (and wasn't that demanding for things after a plug in any event) - e.g. a single 2.5mm² c.p.c. in the flex for 16A plugs and 4mm² for larger plugs appears to be deemed acceptable.

       - Andy.