What should the code be for a Socket circuit supplying a Data Cabinet/Server up to 32a that has no 30mA RCD protection?
What should the code be for a Socket circuit supplying a Data Cabinet/Server up to 32a that has no 30mA RCD protection?
Depends if there's a documented risk assessment...
- Andy.
In the absence of a documented RA..
C3 ?
If you like the feeling you are not alone, in this example for something else, Napit codebreakers say C3 if only used to supply equipment indoors and C2 if it might be used to plug in something outdoors.

your customer can make the C3 vanish by
1) adding an RCD or
2) suitable paperwork (RA and some instructions) and labeling or
3) by changing the plug and socket for a 63A one.
Mike
Presuming the cabinet has a protective conductor current of > 9mA (531.3.2 (c)) - which is pretty likely except for the smallest or mostly unpopulated racks - then a 30mA RCD wouldn't be appropriate - so C3 for lack of a risk assessment to omit one (or alternatively hard-wire it, but that often brings in more safety problems where IT gurus need to move things about).
- Andy.
It is understandable (because of high protective conductor currents, unwanted tripping etc.) why someone would want to omit an RCD for a 32 A socket-outlet that is intended to supply a data/server rack.
Regulation 411.3.3 permits this, provided a risk assessment is in place.
Guidance Note 5 (Section 8.2.3) provides some guidance of what sorts of mitigation ought to be in place where consideration is being given to undertaking a risk assessment to omit an RCD for a socket-outlet ... in this case, whether additional bonding is in place within the data/server rack, and for the data/server rack in the particular room.
omit an RCD for a 32 A socket-outlet that is intended to supply a data/server rack.
That is fine IF the data/server rack uses an UPS (Uninturupted Power Supply) but a lot don't have a UPS
That is fine IF the data/server rack uses an UPS (Uninturupted Power Supply) but a lot don't have a UPS
That's puzzled me - what's your thinking here? A UPS typically won't provide separation from the mains/earth so not really a substitute for shock protection precautions, nor are they much use against nuisance tripping as they'll only support the loads for a limited time (often only a few tens of minutes) - so likely still things go down before anyone can realise and get to the RCD to reset it (especially out of hours).
- Andy.
That is fine IF the data/server rack uses an UPS (Uninturupted Power Supply) but a lot don't have a UPS
I'm not in agreement ... the presence of the UPS might heighten the need for RCD protection on the UPS output in cases where there is no supplementary earthing in place, because the earth fault path is lost when the plug supplying either the rack or the UPS is removed !
I'm not sure if you initially had typo in the polarity of the logic of the greater than sign , and the mostly empty rack, but in any case I agree with the sentiment.
If there is a lot of CPC current due to many things with filters and so on, then you really cannot have an RCD, so one has to try to provide an equivalent level of safety another way.
Commonly this is by additional bonding so recover the normal condition that a single 'off earth' fault does not make anything immediately dangerous, or the equivalent of placing out of reach by controlling the access, or by monitoring the earth continuity electronically and sounding an alarm if it fails . The choice of what is best in any given situation rather depends on the technical knowledge of users and who exactly has access and how often - some server racks are more or less locked in a cage for years and never moved, others are handled every day.
Mike.
I'm not sure if you have typo in the polarity of the logic of the greater than sign , and the mostly empty rack
Opps - well spotted - corrected now
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site