Earth Loop Test

Our ground floor extension has 7x 12v Halogen with the necessary 240v to 12v transformers on a circuit from the wall switch. I would like to upgrade to integrated LED lamps. I understand that if I am competent, I can exchange the fittings and still be within the Building Regs rules. The new LED lamps (Collingwood H2 Lite CSP) need an earth connection.

The existing round 5A junction boxes have an in and out for the circuit (1mm twin and earth) and a feed to the transformer for each light (the transformer doesn't require an earth connection).

To verify the earth connection, I have removed the junction box and transformer for the lamp at the end of the circuit, and temporarily connected a 13A 3 pin socket and I have plugged in a KewTech Loopcheck 07. The KewTech reports all the connections are present, (so earth is connected for the circuit), but it is saying "Check loop test" because it has detected a safety earth path between 1.80 ohms and 92 ohms. 

If I plug the Kewtech into a proper 13A power circuit, it reports everything is OK.

My questions

a) Could the 240v / 12v transformers that are before the Kewtech cause an impedance issue?

b) Could one of the junction boxes have a non perfect connection and therefore cause an impedance issue?

c) Is the use of the Kewtech on a lighting circuit a valid test?

I could move the temporary 13A socket to the start of the circuit, not connect the outgoing circuit and use the Kewtech at that point. If it said everything was OK, I could work around each lamp until the Kewtech complains. 

Alternatively, I could look at a solution that doesn't need an earth connection but since the Kewtech has found an issue, it would sit in the back of my mind. 

Thank you

 

 

Parents
  • Quote “The KewTech reports all the connections are present, (so earth is connected for the circuit), but it is saying "Check loop test" because it has detected a safety earth path between 1.80 ohms and 92 ohms.”.

    The answer as to why the range limit is 1.80 ohms is actually fairly obvious if you think about it and have a look at the tables in BS7671 and other guidance.

    2.3 X 80%=1.84

    and it is a 13-amp socket tester.

    • when the plug is removed; or
    • if someone has put a non-standard 15 A device in place of the 13 A fuse in the plug; or
    • has wrapped tin-foil around the fuse; or
    • has replaced the fuse with some studding or threads of a bolt of a similar diameter; or
    • for "wall-wart' type plug-in appliances (like the socket-tester itself)!

      I see all of those apart from the last  as pretty extreme deliberate actions that are undeserving of full ADS protection, normally done by folk who really ought to know what they are doing, or arguably know better. (and you missed the re-assembly of a plug with 2 neutral pins as another common wheeze for the amateur welder ) Its not many steps away from unscrewing the socket front and wiring to the back of the thing (also seen sometimes at the shallow end).

      Wall-wart devices that are to the correct standards must include their own protection, such as thermal fuses in transformers, or deliberate weak-links in PCBs or even (god forbid) in the good ones real fuses. The fact that cheap far eastern imports exist that sometimes don't does rather undermine the safety case however.

      This sort of plug-in tester is not really meant to fully replicate the array of testgear in the professional's armoury, but is meant to warn  the handyman from using a socket or an extension lead that may appear to work but might be hiding a potentially dangerous fault. As such occasional false alarms are inevitable, and accepted as being preferable to false safe indications.
      Mike.

      PS these are a fun thing for those who enjoy the warmth of a real fire in the living room, given that a 13A plug gets pretty warm above 10A already.
      Available on a well known auction site. No, I'm not posting the link..


  • Even if you spend £280 on the fancy Megger socket tester, you cannot use it for certification purposes, as it cannot be calibrated.

  • Which sort of begs the question of who is it intended for - I could make you a DIY grade one with 2 neons and an RCD test  push button with a BOM cost of about £5-£10 and this is far too pricy for that market segment, yet rules itself out of the professional league.

    M.

  • The story goes that the first socket tester was made by a plumber who lived in Cheltenham, whose hobby was electronics, using a plug, some neons and resistors, and that where he went wrong was selling the design outright to a test equipment manufacturer instead of taking a royalty off each one sold.

  • PS these are a fun thing for those who enjoy the warmth of a real fire in the living room, given that a 13A plug gets pretty warm above 10A already.

    Yes ... BS 1363-2 doesn't cover ratings above 13 A; having said that, if the fuse were to otherwise align with the standard, the dissipation at the rated current of the fuse is limited to 1 W. so the fuse itself ought not to contribute as much to the heat; however, pulling more current through of course will cause products to overheat.

  • What that Megger socket tester does, that installation testers do not do, is measure harmonics to the 49th.

  • has replaced the fuse with some studding or threads of a bolt of a similar diameter

    A chum of mine turned up a very neat little brass bar to the exact dimensions of a BS 1362 fuse when he got fed up with his compressor blowing them on start-up. One might argue that it is little different from fitting a BS 60309 plug and socket.

  • Got one of them; hand made, probably 45 years old.Still detects the occasional loose earth (double socket, end of a long spur; now a proper ring with electricians cert!)

    Plus a baby light in soothing orange neon in a plastic shield protruding from cable grip.

    Grimacing

  • One might argue that it is little different from fitting a BS 60309 plug and socket.

    I don't see too much problem on a 16 A or 20 A radial, as with standard socket-outlet circuits in many EU countries ...  but on a 32 A ring final, of course things can go wrong.

    A chum of mine turned up a very neat little brass bar to the exact dimensions of a BS 1362 fuse

    Cutting an inch of 6.3 mm nominal diameter brass bar often measures up very well when you get the calipers out, as I've done myself for some lab tests on samples of products intended for BS 1362 fuses. From Clause 5.8 of BS 1362:

  • One of my lady customers had a Karcher commercial pressure washer that was blowing the 13-amp fuses, the motor needed a capacitor replacing, once it had a new motor capacitors she didn’t have anymore issues with it.

Reply Children
No Data