Consider a relatively large steel portal frame building in a remote rural location which is used for metal fabrication. The building has had several extensions over the years. Unfortunately, the DNO supply could not be enhanced to meet the growing needs of the enterprise. An upgrade was an eyewatering sum.
There is an original DNO 100A TPN supply which feeds several fuse boards around the building, a 500KVA generator supplies a large piece of machinery and a 100Kw inverter with solar PV and batteries supplying two TPN MCB boards to various items of plant. There is no grid supply to the inverter. The inverter has a NE bond and uses the steel frame as an electrode as does the NE connection on the gen set. The DNO earth is PNB and also bonded to the steel frame.
There is plenty of equipment and opportunity for simultaneous contact with different disconnection time requirements. I haven't done any detailed analysis of touch voltages, but is this all I need concern myself about in terms of fault protection?