Singles and Data in the same Dado trunking compartment

What are peoples thoughts on mixing 230V 6491B singles and standard structured wiring data cables in the same compartment of Dado trunking. Although the case I am involved with are supposedly only running next to each other for a short distance it clearly doesn't comply with 528.1 Proximity to electrical services. I have a contractor that isn't concerned by this, however even if the client agrees with a departure from BS7671 I'm still concerned from a health and safety perspective as many of the instances of this are in a medical location.

Parents
  • Thanks for the replies. I also note the following from 120.3

    "Any intended departure from these Parts requires special consideration by the designer of the installation and shall be recorded on the appropriate electrical certification specified in Part 6. The resulting degree of safety of the installation shall be not less than that obtained by compliance with the Regulations."

Reply
  • Thanks for the replies. I also note the following from 120.3

    "Any intended departure from these Parts requires special consideration by the designer of the installation and shall be recorded on the appropriate electrical certification specified in Part 6. The resulting degree of safety of the installation shall be not less than that obtained by compliance with the Regulations."