Do you need to install an RCD on a circuit for alterations or amendments to Lighting circuits that now include outside lighting?

Following amendments to a circuit and installation of additional lighting (emergency) externally, is there a requirement for 30mA RCD protection on the circuit? 

Under section 714 - regulation 714.411.3.4 Additional Lighting - except for lighting supplied from a SELV source, lighting is accessible to the public shall have additional protection by an RCD having a rated residual current as specified in Regulation 415.1.1 which states use of an RCD with residual current not exceeding 30mA.