Why are we still using ring final circuits?

Hi all, I wanted to discuss the use of ring final circuits in electrical installations in the UK. 

I am an electrical contractor based in Surrey, England and, though I have predominantly spent my 20 year electrical career in the industrial sector, I have recently found myself in the domestic installation world - which has really opened my eyes to, what I believe to be, certain dangers of this installation practice here in the UK. I'd like to share two recent scenarios I have encountered domestically.

Scenario 1

I was called to a customers house to investigate a fault which was preventing the customer from switching on her 32A MCB without it immediately tripping. Upon beginning my investigation, I immediately discovered that the ring circuit in question had no continuity on both the Line and Neutral conductors. I also noticed that various sockets on the ring circuit had a black, sticky residue seeping from all 3 terminals of each outlet. After locating the fault causing operation of the MCB, I returned to the case of the broken ring continuity. I discovered that the Line and Neutral conductors had broken behind a countertop socket in the customers kitchen. It then became apparent that all sockets with the residue were sockets on the leg of the ring leading up to the broken point. Along this route were sockets feeding every appliance and piece of equipment in the kitchen, so my assumption is that the load, and subsequent heat, on this leg of the ring must have caused the insulation to deteriorate so and seep out from the terminals. 

Scenario 2

I was asked to install a few extra sockets onto an existing ring final circuit in a customers house to provide a newly built entertainment unit with several socket outlets. Immediately, I isolated the power and tested for ring continuity of the existing circuit only to discover, again, that the Line and Neutral conductors were not continuous. After a short investigation I discovered, much to my own and my customers horror, electrical cables protruding from a box with insulation stripped and copper conductors free to the touch. Whoever had removed an electrical accessory must have completely forgotten to return and re-connect it before turning the power back on. The scary thing about this one is that it was tucked away in a cupboard that my customers 8- and 10-year old sons kept their bike helmets - which the used every day to get to and from school. 

Both of these scenarios frighten me a little in the sense that these faults lay completely hidden and undetectable from untrained eyes. Because of the configuration of the wiring, nobody could tell that anything was wrong with the circuits, or that possible danger lay in wait. Does this not pose a huge, yet unnecessary, risk? To me there's absolutely no reason that we still need to be installing these circuits in 2026.

I personally feel that the industry as a whole might have gotten a little lazy. Showing up and installing numerous rings seems, to me, to be lazy design. Though I don't feel we're being taught any different. My apprentice informs me that they're still learning about them in college at the moment. Isn't it time we started designing our installations more efficiently: dedicated circuits for fridge/freezers, washing machines & tumble driers, induction hobs etc, 20A radials for ordinary sockets? Or, am I wrong? 

At the very least, if this kind of fault occurs on a radial circuit then some points - at the very least one - will cease to work and give the user of the system an indication that something is wrong. 

Does anyone agree?

Parents
  • Scenario 2 could have happened even if it wasn't a ring so don't see the relevance of it to be honest.

    Both Scenario's were caused by someone not doing their job properly or a DIYer.  Scenario 1 might have become apparent earlier if it was a radial. 

    99% of problems I come across on installations are after someone has messed about with it who was not qualified or competent to do so.

    Personally I don't see the problem with rings when done properly but then it's all I've known and I'm a bit of an old git now. Things change, although I doubt rings will.  ( I know it's a ring final Slight smile )

    Gary

  • I think it is completely relevant. There were numerous sockets on either side of the disconnected point both making their path back to the consumer unit. If it was a radial circuit then whichever side of the circuit was downstream would have ceased to provide any power and this would have been quickly apparent to the customer, prompting them to get some assistance. However, because it was installed as a RFC, nothing appeared to be wrong and the bare conductors remained like that for at least a year since they moved in. And, I've heard it many times that "if they are installed properly and well maintained then they're perfectly fine". But I think we all know that domestically, this isn't always the case. Handymen and DIY'ers are allowed for too much freedom to meddle in our trade. We live in quite a dangerous age at the moment where electricians are posting videos online (for likes and popularity, I can only assume), encouraging those who are not qualified to venture into our world of electrical installation and maintenance.

Reply
  • I think it is completely relevant. There were numerous sockets on either side of the disconnected point both making their path back to the consumer unit. If it was a radial circuit then whichever side of the circuit was downstream would have ceased to provide any power and this would have been quickly apparent to the customer, prompting them to get some assistance. However, because it was installed as a RFC, nothing appeared to be wrong and the bare conductors remained like that for at least a year since they moved in. And, I've heard it many times that "if they are installed properly and well maintained then they're perfectly fine". But I think we all know that domestically, this isn't always the case. Handymen and DIY'ers are allowed for too much freedom to meddle in our trade. We live in quite a dangerous age at the moment where electricians are posting videos online (for likes and popularity, I can only assume), encouraging those who are not qualified to venture into our world of electrical installation and maintenance.