Hi all
I’d like your opinion on the following setup please. Last year wired a storage outbuilding for a customer comprising lights, sockets, roller door etc. The supply to the whole premises is single phase TT. I ran a supply from the meter position via a 100mA time delayed rcd and 63a mcb to a distribution board in the new building. The customer has since built two extra buildings adjacent to the first building, a mechanics workshop and a storage shed. I have installed two distribution boards in the mechanics workshop to supply it and the storage shed. My question concerns the earth fault protection for the distribution circuits. The building wired last year has a distribution board containing a main switch and rcbo’s. I ran a supply from this board to the first board in the mechanics workshop via a 50a mcb. The board in the workshop then contains rcbo’s for all the final circuits. I then ran a supply from the first board in the mechanics workshop to a second board via a 40a mcb in the first board. The second board contains rcbo’s for all the final circuits. As it stands the earth fault protection for all my distribution circuits is provided by the 100ma time delayed rcd at the meter position. Is this acceptable or should I install an rcbo in the first board to supply the other two boards? This then means that everything in the new buildings is on one 30ma rcbo which isn’t very practical, nuisance tripping etc. is it acceptable for distribution circuits to have fault protection via the main rcd at the meter position?
thanks
Peter