I'm interested in hearing how others apply BS 7671 thermal insulation derating factors in practice when cables only pass through a relatively short section of thermal insulation or fire stopping.
BS 7671 Appendix 4 provides derating factors for cables surrounded by thermal insulation, and in some cases the resulting reduction in current-carrying capacity can be significant. However, many building installations only have cables passing through localised fire-stopped penetrations, fire collars, fire pillows, or fire batt systems, typically over a short distance compared with the total cable run.
My question is:
Do you apply the thermal insulation derating factor to the entire cable length and its current-carrying capacity, or do you consider the effect to be more localised?
From a heat transfer perspective, the highest cable temperature will occur within the insulated/fire-stopped section, but heat can also be dissipated longitudinally along the conductor and sheath into adjacent cooler sections of cable. This suggests the thermal behaviour may not be equivalent to a cable being continuously surrounded by thermal insulation over its entire length.
Has anyone come across:
- Guidance from BS 7671, IEC 60364, ERA reports, manufacturers, or DNOs on this specific situation?
- Any accepted industry practice for short fire-stopped penetrations?
- Thermal modelling, testing, or engineering assessments that justify a less conservative approach than applying the full derating factor to the complete circuit?
I'd be interested in both the theoretical basis and how designers, contractors, and reviewers typically approach this in practice.