I am proposing to build a new garage-workshop. Based on current cost estimates, this will be metal-framed and clad, on a concrete base.
The proposal is to install 12 to 14 solar panels on the roof and a Tesla Powerwall in the garage. And yes, this installation will need a G99. The panels are DC-coupled to the Powerwall.
The garage will have two separate circuits from the meter area in the house (as recommended by the installer)
- Cicuit feeding an EV charger, 3-core SWA
- Circuit connecting the Powerwall, 3-core SWA
There will also be a local consumer unit in the garage, connected to (b) to feed lights, sockets, power tools etc.
The plan is for the builders to install the cabling to leave tails, and then the installer will install and connect the electrics. Even though SWA cables will be used, the plan is to install these in a duct for future proofing where this crosses the garden
I’m also likely to install a fibre data cable. This may also be SWA but I wasn’t proposing to connect the armour, it’s only for mechanical protection. This is mostly to avoid the latency of a WiFi link.
The supply to the house is TN-S with Zₑ 0.24 Ω
My only query about this installation is the earth bonding of the garage structure & cladding metalwork. I’m assuming that the structure’s frame components will need to be earth bonded and perhaps also the cladding panels – does this sound about right?
Would the garage likely need a local earth rod – or is it preferred to use the extended supply earth?
One of the reasons that the earthing is of interest is that the garage may have some ham radio equipment. My practice is to power such radios from a 12V battery charged by a charger where mains earth is not bonded to the 12V negative rail. A local clean RF earth is then used, and it’s undesirable to have this close to a mains protective earth rod.