- Written confirmation is provided confirming the existing main protective bonding connection and conductor size to the mains water service; or
- A new main protective bonding conductor is installed to the mains water service, where such bonding is required.
“Whilst there is no obligation to inspect and test any part of the existing installation that does not affect and is not affected by the addition or alteration, any departures or non-compliances observed are required to be noted in the ‘Comments on existing installation’ section…”
-
Does Regulation 132.16 prevent an EIC from being issued for an addition/alteration solely because the presence or adequacy of an existing main protective bonding conductor to the water service cannot be verified, where that part of the existing installation does not affect and is not affected by the addition/alteration?
-
How should it be established whether the existing water bonding arrangement is relevant to the protective measures applicable to the addition/alteration for the purposes of Regulation 132.16?
-
Where the lack of required main protective bonding is an existing-installation deficiency but does not affect the safety of the new work, can the existing deficiency be recorded in the “Comments on existing installation”on Form 2 while still issuing the EIC for the compliant addition/alteration?
-
Separately, if an Electrical Installation Condition Report (EICR) is undertaken and the inspector determines that required main protective bonding is absent and constitutes a potentially dangerous condition, can this be classified as C2, where technically justified, resulting in an overall “Unsatisfactory” assessment?
-
Is there any other caluse in BS 7671 Regulations and/or IET Guidance Note references that should be taken into consideration?