The customers buried TT earthing system shall be segregated from the WPD buried earthing system (including buried LV metalwork and traditional Paper Insulated Lead Covered cables) by the required distance
Single Phase or Unbalanced 3 Phase Connection 3.6m
Balanced Three Phase Connection 0.3m
6.5 The Electric Vehicle Charging Point (whole installation) shall be segregated (above ground) from metalwork connected to PME or SNE earthing systems by at least 2.5m e.g. metallic street lights and steel frame buildings.