is there any online EV charger supplier in UK who can ship EV chargers with PEN fault protection to India?

is there any online EV charger supplier in UK who can ship EV chargers with PEN fault protection to India? 

Parents
  • Going off on a slight tangent - would UK style open-PEN units work reliably on the Indian system? Most work on the assumption that the L-N voltage is within UK ESQCR limits and if it drifts out of that will trip out presuming a PEN fault. UK limits are between 216.2V and 253V at the supply - with open PEN units tripping out if the voltage goes outside 207V...253V which allows for some normal voltage drop within the installation. I gather that the Indian spec is for down to 207V at the supply so even in a compliant installation it could well be a lot lower than 207V at the charge point - risking a lot of false tripping. Some have even suggested that in practice Indian supplies might not always be entirely compliant with specifications either.

    Does India use PME/TN-C-S?

        - Andy.

  • would UK style open-PEN units work reliably on the Indian system? 

    No it wouldnt . We need this only for research purpose. We will have a variable power source and try understanding the PEN fault circuit.

    Most earthing in India uses TN-S system

Reply
  • would UK style open-PEN units work reliably on the Indian system? 

    No it wouldnt . We need this only for research purpose. We will have a variable power source and try understanding the PEN fault circuit.

    Most earthing in India uses TN-S system

Children
No Data