We have found a series of issues whilst performing solar maintenance and testing on a metal framed and cladded building (including the roof). 

The System: 

installed in 2015

442 Panels installed over 22 Strings. Panels installed JA Solar - JAM6-R-60/275 JA Modules  

The system is 3 phase and comprises of four 20kW three phase inverters (AC coupled)

No Batteries on site. No earth spikes found. The PV array frames and mounting are directly attached to the metal structure 

The DC string voltage ranges from 700-800V DC on the healthy strings. No string surge protection. No string over current protection. Just panels directly connected to inverters via 4mm solar PVC cables

System Condition: 

Many panels are damaged/broken. Some with holes tennis ball size in. Heavy seagull damage. Lots of fauna growing between panels.

Site weather conditions: 

Foggy and Raining 

The Fault:

Of the 22 Strings 17 have faults to earth. Insulation Resistance tests (1000V DC test voltage) were attempted from both Positive and Negative MC4 connectors (taken out of the inverters) to earth (the structure). The IR test was not possible as we were getting 600-800V from both positive to earth and negative to earth. We do find voltage during these test normally, but it generally dissipates down to a level were we can test within 2-10 seconds. This is commonly known as a RISO issue, i'm aware. On the healthy strings we were getting 0.1 - 3 Mohms. 

I'm aware we can test which panel is likely causing an issue by taking the volts present between P-E and dividing this by the individual panel Voc. 

My question is: 

Even with the inverter DC isolators in the open position (Off), on all 22 strings, is there a risk to life or a chance of fire with the system in its current condition.

Does the building structure pose a risk of electrocution?  (nearest building 35m). Trucks and vehicles are operating within the building 12 hours a day.

Fault example: If we had a P-E fault on panel 1 of 20, and a negative to earth fault on panel 20 of 20 you could get a short circuit.

Action taken:

We have issued a danger notice whilst we investigate this further. This was suggested by our accrediting body as well. They are currently looking at this with us to help find a solution. 

Any thoughts or solutions welcome. 

 

Parents
  • RISO (Resistance Isolation warning - 'translated from the foreign') is what the better inverters report when there is a connection to earth in the middle of the string of photodiodes on a panel ) In a panel with puncture damage, this is quite believable.

    Panels are inherently current limited - you will never get more electrons per second than photons that land on the thing - in practice quite a lot less. But faulty panels are a bad thing, and the partial earthing means that things that should float wrt earth will not, and may well be capable of if not electrocuting someone, at least throwing them to the extent they drop off the roof, which  is just as serious. And the inverter will not be able to make use of their output.

    Lay off the meggar - it will not take sensible readings and may damage good panels which are essentially strings of low voltage diodes each one generating half a volt or so open circuit.
    A more useful test is to look for a voltage between wires and frame, with some sensible load - in the old days a test lamp, maybe now a resistor. Anything voltage line to frame that does not fall away to be just a few volts once a  load has been connected in parallel with the meter is a sure sign of a mid-string fault.

    The only sensible thing to do is to all-pole isolate or  unplug the obviously damaged panels, and if you have to remove them in daylight, then you should reduce the output current available by covering  the active surface, and treat the wire tails and any exposed damaged panel regions where the seagulls have landed (*), as if they might be  live relative to the panel frame.

    Tricky one, I do not envy you.

    Mike

    * Seagull has landed sounds like a line from a Mike Myers movie - a low grade version of " The eagle has landed"

  • Thanks for the response. Helpful comment. The IR test was not possible due to the voltage between positive to earth and negative to earth (the structure) readings of 600-800V present on all of the 17 faulty strings. I'm trying to make sense of the risk factors at play. Adding additional parallel faults from the other 16 faulty strings to the mix only raises my concerns.

    We are in the process of implementing access equipment to start disconnecting panels to reduce the overall voltage of the strings. 

    Keen to understand the risks in this sort of scenario in more detail. It's a common fault after all.

    Many thanks!  

Reply
  • Thanks for the response. Helpful comment. The IR test was not possible due to the voltage between positive to earth and negative to earth (the structure) readings of 600-800V present on all of the 17 faulty strings. I'm trying to make sense of the risk factors at play. Adding additional parallel faults from the other 16 faulty strings to the mix only raises my concerns.

    We are in the process of implementing access equipment to start disconnecting panels to reduce the overall voltage of the strings. 

    Keen to understand the risks in this sort of scenario in more detail. It's a common fault after all.

    Many thanks!  