Solar Energy Systems installation UK - lack of skills

As I researched Solar Energy systems for over a year now I discovered how little I understood the dangerous realities of Solar installations even though powered at ELV level <50Vdc.  The difference being that you are dealing with a constant current of 50 - 100's A dc.  Average Joe, maybe used to Auto/Truck 12/24Vdc  systems probably sees the system as safe - you dont get a shock (boat owners will disagree).  So the hazards of installing a dc distribution system  within a domestic house and the potential to cause disastrous fires are totally underestimated.  Even the average tradesman electrician will not have sufficient training in such matters in his CPD scheme.

To make matters worse, as a result of a question by a neighbour who want to suggest to his lad that he follow an Electrician apprenticeship, I discovered that my area (SE UK) has no regular Technical College Route pursuing CnG courses.  Apprenticeships are very rare and as a rule focus on training junior managers. 

In short, a young person cannot readily find his way in to becoming and electrical tradesman ( I have to make a distinction between the concept of a Technician here)

When you aggregate the complete installation identifying all physical components, the SLD suddenly becomes quite complex.  ie Going from Panel Arrays > optomisers > cables > marshalling boxes > Fuse links > Isolators > Master Circuit Breaker > Inverter (s) > Battery Bank > Domestic Consumer Unit > Grid resale meter > Master Isolator > standby generator > Auto Transfer Switch, Control and monitoring systems, Emergency shutdown scheme.

When you seen the numerous wannabee hopefuls going offgrid and often their lack of formal technical training they dont realise how dangerous their rough and ready installation is

I can post links to many sources of my concern here if there is sufficient interest

Robin 

Parents
  • Yes ELVs <50Vdc.  IMHO its sheer madness to be involved with MV dc Panel strings - way too dangerous  IMHO in a domestic environment, and we dont have the skilled tradesmen to recognise this type of micro grid nor is there a recognised route to upgrade to this unfamiliar but hazardous system.  Way too many unschooled wannabees playing with fireworks.  It is utter negligence by our Political leaders to allow this to continue.  They only woke up to the hazards of amateur plumbers who didnt understand flammable atmospheres till a few houses were blown up flattened.  Then British gas had to step in a institute proper training courses with local tech colleges.  Where do our Electricians get proper upgrades?  A one man jobber cant afford an apprentice (with all the paperwork and oversight involved). He will only have a family member or friend involved.

  • Agenda!!!!!!!!!!!!  I am crying out for amateurs to get themselves properly educated instead of the painful "suck it and see" attempts shown on youtube by technically illiterate bluffers pumping out dangerous practices for the credulous public to play with.  Its as bad as showing kids how to make fireworks.   Perhaps you havent browsed enough of these crass vids to see how misleading and dangerous they are.

    Maybe just sit back and let the inevitable tragic accidents occur 

  • More homework needed here old chap. FYI you cant sustain an arc flash at 12 V.

    Indeed ... although I think we know enough already. It's possible to cause an arc at 12 V DC (not AC) from two conductors in direct contact (we know this from car batteries) ... although it does "blow itself out" as the gap increases as the conductors melt.

    Things can get interesting, though, with "constant current source" behaviour of solar panels and power converters.

    We are talking "arc" and not "arc flash" here, and I would agree 100 % that we don't start to get too many problems with arc flash at 12 V DC, perhaps up to 24 V DC.

  • No young engineers or electricians receive any specific instruction in the nature of ELV dc distribution

    More accurately, I believe it depends where you've been employed in industry. Power supply to controls and telecoms (and 'telecontrol') never went away from ELV DC ! However, I agree in general, when we talk about "electricians" the industry moved away from DC in the 1960s, but it's coming back now !

  • Agenda!!!!!!!!!!!!  I am crying out for amateurs to get themselves properly educated instead of the painful "suck it and see" attempts shown on youtube by technically illiterate bluffers pumping out dangerous practices for the credulous public to play with.  Its as bad as showing kids how to make fireworks.   Perhaps you havent browsed enough of these crass vids to see how misleading and dangerous they are.

    Maybe just sit back and let the inevitable tragic accidents occur 

    I wouldn't just limit to amateurs.

    Solar power is now mainstream.  Houses all over the country are covered in solar panels.

    Yes, and DC battery storage is happening quickly too.

    They work, and it's very rare that anything bad happens.

    I would be a little more cautious here, especially given some insurance companies' views aired in the past 12-18 months. But I would accept that's not "DC power cable fire risk" alone ...

  • Once again I find myself at odds... as a kid who actually did make fireworks, and indeed in the 6th form we made gun-cotton, sufficiently well to damage the greenhouse of the parents of one of my friends, there is a lot to be said for learning by doing.

    We also got up to a lot of stuff that nowadays would be more than just frowned upon, but we also learnt a lot very fast and remained largely intact, and the one who did not was due to a moped accident.

    To my mind the error  of modern society is to infantalise the 'consumer' and assume they are incapable of understanding and making any technical decision as if consumers are some blobby mass incapable of doing  anything more complex than signing a cheque,.

    Some may be , but the rest really should have access the resources,  to find out how to do things well, and then allowed to either  get on with it themselves or to instruct an installed to do what they want. (I'm the sort of customer who comes at the tradesman when he arrives every morning to make sure that what he intends to do today matches my plan, not the other way round . )

    The alternative is a sort  of societal brain rot. This I see it in many places,  folk in their 20s who cannot change the wheel on their car - fine if you live inside the M25 so you are within 20 mins of an AA truck and in an area of good phone coverage, terrible if you are on hols in the Scottish highlands,.. teenagers who do not know how to catch a bus, adults who cannot read a map.

    I do not care if folk learn in a formal setting in a classroom or by the more traditional watch one do one teach one. but they do need to learn

    Mike

  • To my mind the error  of modern society is to infantalise the 'consumer' and assume they are incapable of understanding and making any technical decision as if consumers are some blobby mass incapable of doing  anything more complex than signing a cheque,.

    Not sure what that has to do with what we're talking about?

    For example, is it OK to put gg type fuseholders in accessible places on battery storage systems in homes that can be simply "pulled on load" by anyone ... including children? Similarly, sitting series/parallel monoblocs without internal overcurrent protection on the floor (for example in the garage or even on boards in the loft)??

    Because that's what's happening in some ("not amateur") installs?

  • And an educated customer or a customer who's friends felt able to offer an opinion would pick up on this and say 'that's not right' much as we all know helpful folk who will tell you that your car has a problem - even if as in  my case you already know.

    Thus the wider educated collective can correct - being a far better policeman than some trade body that looks at a few jobs a year that are within a short drive and easy to look at, where a large part of their aim is to keep the subscription payment flowing.

    Mike.

  • And an educated customer or a customer who's friends felt able to offer an opinion would pick up on this and say 'that's not right' much as we all know helpful folk who will tell you that your car has a problem - even if as in  my case you already know.

    Thus the wider educated collective can correct

    I do take that point in general. But that doesn't appear to be happening with Solar & Battery installations.

  • I was astonished to see a well known US brand which supplies a complete solar kit down to the inverter mains outlet use a rotary cam switch (typically seen on electrical panels) as a circuit breaker between the panels and the Inverter  (no internal arc quench in that design).

    A simple rotary isolator between PV panels and inverter is a pretty well accepted way of doing things. It's only intended as an off-load isolator to allow work on the inverter. PV panels, unlike mains or large battery supplies, are incapable of producing large currents (it's limited by sunlight) - even into a dead short the maximum expected is 125% of normal output current. Oversize your PV d.c. cables by a little and no overcurrent protection is needed in a simple system.

    Introducing batteries does introduce the potential for much nastier problems of course, but the charge controller would usually prevent backk-flow from the battery to the panel circuit.

       - Andy.

  • even into a dead short the maximum expected is 125% of normal output current

    That's more than sufficient current to draw an arc, and sustain it for some considerable period of time (for example as an MC4 burns and disintegrates). WIth currents as low as 1-2 amperes !

    In fact, if there is a fault, because they do happen, what is built into a solar PV system to enable someone to work on the system safely, or remove the arc etc.? Usually nothing!

    For safe working on Solar PV, isolating at the inverter may stop current flow ... but what are the consequences if it didn't (say because there's a fault L+ to L- between the panels and in the inverter)? The only way to check for this, is to check for DC current flow with a DC current clamp meter at the point of disconnection, prior to disconnecting (because there's nowhere to "prove dead").

    If not, these are the potential consequences: youtu.be/rkq1zwG9vLc

Reply
  • even into a dead short the maximum expected is 125% of normal output current

    That's more than sufficient current to draw an arc, and sustain it for some considerable period of time (for example as an MC4 burns and disintegrates). WIth currents as low as 1-2 amperes !

    In fact, if there is a fault, because they do happen, what is built into a solar PV system to enable someone to work on the system safely, or remove the arc etc.? Usually nothing!

    For safe working on Solar PV, isolating at the inverter may stop current flow ... but what are the consequences if it didn't (say because there's a fault L+ to L- between the panels and in the inverter)? The only way to check for this, is to check for DC current flow with a DC current clamp meter at the point of disconnection, prior to disconnecting (because there's nowhere to "prove dead").

    If not, these are the potential consequences: youtu.be/rkq1zwG9vLc

Children
  • For safe working on Solar PV, isolating at the inverter may stop current flow ... but what are the consequences if it didn't (say because there's a fault L+ to L- between the panels and in the inverter)? The only way to check for this, is to check for DC current flow with a DC current clamp meter at the point of disconnection, prior to disconnecting (because there's nowhere to "prove dead").

    Indeed, a good point raised here - how to tell if a dc cable is dead.  Analogy the ubiquitous neon screw driver owned by every Leccie, automatically check for a live wire before intervention (also the bare knuckle test some believe is more reliable as your neon could fail)

    So what is proposed here is that compulsory use of a Hall Effect clamp meter on solar cables before intervention.

    BUT  the sad thing here which my OP highlighted is that we dont have any formal training worth a damn to promote theis level of Safety Training

  • BUT  the sad thing here which my OP highlighted is that we dont have any formal training worth a damn to promote theis level of Safety Training

    Agreed ... not everyone has the relevant training and experience.

  • That's more than sufficient current to draw an arc

    Indeed, but nothing a d.c. circuit breaker towards the inverter end would do anything to help. I don't think we have DC AFDDs available yet (and no obvious place to position one in a PV string either). I guess it's back to the very old school methods - insulation, sheathing, maybe put +ve and -ve in separate conduits etc and keep some physical space between them(*) to manage the risks of parallel arcs.

    * but not too far apart, we don't want a big loop, for EMI reasons.

       - Andy.