HV Safety advice required

Hi, 

Contemplating the safest way to carry out a HV switching program

We're carrying out function checks of an existing 11kV VCB, we have two options:

  1. Switch off, rack out into a test position (only control voltage applied) and manually operate on a dead system, and then rack back into the live connections or:
  2. Switch the downstream load off, so the circuit is energised with no load and perform manual switching in front of the energised VCB

Personally I see both as having pitfalls, however I am uncertain whether manually switching 11kV VCB under no load is safer than racking into and out of live busbars

Any other important considerations to be taken into account?

Regds

Parents
  • Do you have appropriate arc flash protection clothing? It's not perfect but it can be helpful if something goes wrong.

Reply
  • Do you have appropriate arc flash protection clothing? It's not perfect but it can be helpful if something goes wrong.