I am currently sizing a Standby Generator for Life Safety purposes for an office building. My equation to calculate this is:
Sprinkler Pump Locked Rotor Current + sprinkler pump starting current + starting current of Smoke fans + running current of all other loads (FF Lift, Evac lift and fire fighting core lighting and power).
my question is should I allow for the DOL (Direct on Line) starting current of the Smoke fans, or the VSD starting current? The smoke fan data sheet is below. The DOL start is 7x the full load current. However, I think this should be allowed for as the VSD could fail in a life safety situation. The life safety Automatic transfer switches are likely to be set to time delays so the sprinkler LRC + starting and smoke fans starting are unlikely to happen at the same time, however should this be allowed for?