Impact of negative reactive power or Leading Power factor on synchronous generator

Dear Sir,

We are running with 03 nos. of synchronous Generator(11kv) with following running parameters,

Machine Voltage = 11.100 KV

Excitation Current = 2.5 amps

Machine Current = 182 amps

Reactive Power = - 1.66 MVAr (negative reactive power)

Power factor = - 0.87 leading

Active Power = 3.06 MW

Generator Rating details,

Output - 7287 KVA, Duty - S1, Voltage - 11000V, Current - 383 amps, Power Factor - 0.8 lagging,

Excitor Rated current & voltage - 7.8 amps & 78.9 V

Generator protection relay having trip set point for under excitation protection Q< (40) is -2.16 MVAr with 2sec delay. 

Synchronous generators are running with leading Power factor with -1.66 MVAr reactive power, so what will be the consequences from generator health point of view.  What will be the risk. 

Pls share your comments pls. 

  • Finding the exact value at which instability would occur, requires more information. However, in general, this value of leading power factor is likely to cause under-excitation of the generator which will lead to instability and tripping. You would need to determine the cause of the leading power factor. Are there capacitors that can be switched out? Is it another cause such as long unloaded powerlines or cables - in which case inductive reactors would usually need to be added when load is low.

  • Dear Rohit,

    It seems that the information you have provided about the overall system condition is incomplete. It would be helpful to have a more comprehensive overview of the system, such as whether the negative reactive power is occurring in one generator only or in all of them. Additionally, is your system operating in island mode, or is it connected to the grid?

    Nevertheless, assuming the negative reactive power is limited to one generator, this is typically caused by either the excitation system being unable to supply the required reactive power due to a voltage drop when providing more excitation current, or by the system not responding adequately to variations in reactive power. This results in other generators compensating for the reactive power demand of the system. In such cases, the unequal sharing of reactive power places additional stress on the other generators, potentially leading to damage and adversely affecting the overall system power factor. This issue needs further investigation to prevent damage to other components in the system.

    For the generator operating with negative reactive power, the primary risk lies in pole slipping, instability, and possible tripping, as the generator is functioning in an unstable region within its capability curve. Tripping the machine is undesirable and should be avoided to maintain system reliability. Beyond these risks, other concerns are minimal.