Dear Sir,
We are running with 03 nos. of synchronous Generator(11kv) with following running parameters,
Machine Voltage = 11.100 KV
Excitation Current = 2.5 amps
Machine Current = 182 amps
Reactive Power = - 1.66 MVAr (negative reactive power)
Power factor = - 0.87 leading
Active Power = 3.06 MW
Generator Rating details,
Output - 7287 KVA, Duty - S1, Voltage - 11000V, Current - 383 amps, Power Factor - 0.8 lagging,
Excitor Rated current & voltage - 7.8 amps & 78.9 V
Generator protection relay having trip set point for under excitation protection Q< (40) is -2.16 MVAr with 2sec delay.
Synchronous generators are running with leading Power factor with -1.66 MVAr reactive power, so what will be the consequences from generator health point of view. What will be the risk.
Pls share your comments pls.