Impact of negative reactive power or Leading Power factor on synchronous generator

Dear Sir,

We are running with 03 nos. of synchronous Generator(11kv) with following running parameters,

Machine Voltage = 11.100 KV

Excitation Current = 2.5 amps

Machine Current = 182 amps

Reactive Power = - 1.66 MVAr (negative reactive power)

Power factor = - 0.87 leading

Active Power = 3.06 MW

Generator Rating details,

Output - 7287 KVA, Duty - S1, Voltage - 11000V, Current - 383 amps, Power Factor - 0.8 lagging,

Excitor Rated current & voltage - 7.8 amps & 78.9 V

Generator protection relay having trip set point for under excitation protection Q< (40) is -2.16 MVAr with 2sec delay. 

Synchronous generators are running with leading Power factor with -1.66 MVAr reactive power, so what will be the consequences from generator health point of view.  What will be the risk. 

Pls share your comments pls. 

Parents
  • Finding the exact value at which instability would occur, requires more information. However, in general, this value of leading power factor is likely to cause under-excitation of the generator which will lead to instability and tripping. You would need to determine the cause of the leading power factor. Are there capacitors that can be switched out? Is it another cause such as long unloaded powerlines or cables - in which case inductive reactors would usually need to be added when load is low.

Reply
  • Finding the exact value at which instability would occur, requires more information. However, in general, this value of leading power factor is likely to cause under-excitation of the generator which will lead to instability and tripping. You would need to determine the cause of the leading power factor. Are there capacitors that can be switched out? Is it another cause such as long unloaded powerlines or cables - in which case inductive reactors would usually need to be added when load is low.