Iberien Peninsular Blackout

Any thoughts/information on what happened? Was it a lack of spinning reserve?

Was it " The Portuguese operator, REN, said the outage was caused by a “rare atmospheric phenomenon”, with extreme temperature variations in Spain causing “anomalous oscillations” in very high-voltage lines."

as is written in the Guardian?

Electricity restored to 90% of Spain and most of Portugal after massive power outage | Spain | The Guardian

The Italien blackout from a few years ago had a definate cause in the tripping of interconnetors from Switzerland during a storm.

Parents
  • Many sources in the last 24 hours quoting a Spanish government report, e.g. this from Reuters, but no link to the actual government report.  Has anyone found this?

    Paul Adkins

  • PDF

    The official communique is here.  "Se presenta el informe del Comité de análisis de la crisis eléctrica del 28 de abril"

  • google translate summary and conclusions

    In short, there was a lack of voltage
    control resources, either because they
    were not sufficiently scheduled, or because
    those that were scheduled did not provide them
    adequately, or because of a combination of both,
    but not because they were lacking in the country;
    there was more than enough generating capacity
    to respond.
    MAIN RECOMMENDATIONS
    In light of the conclusions obtained
    from the analysis, the Committee
    proposes a series of actions to
    prevent a recurrence of this type
    of incident. These include
    strengthening supervision and
    verification of compliance with
    obligations by all stakeholders
    in the electrical system, as well
    as technical measures to strengthen
    voltage control capabilities
    and protect against fluctuations
    in the system. Key to this is
    the implementation of OP 7.4, in
    the hands of the National Commission
    of Markets and Competition (CNMC).
    This will allow asynchronous
    installations to apply power
    electronics solutions to manage
    voltage variations and may
    contribute to cost savings with
    the introduction of more competitive
    technologies. Furthermore, it
    proposes increasing demand and the
    flexibility of the electrical system.
    All of this will be supported by
    the 2025-2030 Electricity
    Planning—which will prioritize
    industrial consumption—an increase
    in storage capacity, and a review
    of the regulation of adjustment
    services and the system's technical
    restrictions.
  • Thanks, this makes interesting reading.

    I hope this is not a stupid question: Why would disconnecting generating plant from the grid cause the voltage to increase?  

    Paul Adkins

  • presumably because that generator is actually motoring- or acting as an inertial drag on the system.If you have light loads and embedded generation the traditional slope of the voltage drop from generator to load can be reversed  and in a sense the tail tries to wag the dog.

    Its not a condition you want to persist for extended periods however.

    Mike

  • The issue seems to be about managing reactive power flows. If the service providers who were absorbing VArs trip off, then the remaining excess VArs will raise the voltage across the system

  • - yes no significant real power is generated, rather absorbed at one point in the mains cycle and pushed out in another, but in effect providing a giant power factor correction at grid level.

    I'm also not sure if this includes waveform quality correction here - I suspect the inverter derived wave-forms are a lot dirtier in terms of square edges  than sine-waves from rotating magnets.

    Certainly both the line- and self- commutating thyristor based DC link stations generate some pretty unpleasantly rectangular current bursts and rely on other grid elements to spread what are in effect  current impulses more uniformly across the cycle. In the hopelessly simplified circuit below the upper wave-forms near the in and out terminals illustrate this. (The pale grey sine is voltage and the darker bumpy thing represents the general form of the current into or out of the grid) 

    Instructions always say that a low impedance grid is needed to keep the voltage waveform from becoming more like that of the current. (sometimes expressed as harmonic content vs supply impedance)
    Removing e.g. the French AC connection and leaving a large DC station on would perhaps  have been problematic in this way
    M

Reply
  • - yes no significant real power is generated, rather absorbed at one point in the mains cycle and pushed out in another, but in effect providing a giant power factor correction at grid level.

    I'm also not sure if this includes waveform quality correction here - I suspect the inverter derived wave-forms are a lot dirtier in terms of square edges  than sine-waves from rotating magnets.

    Certainly both the line- and self- commutating thyristor based DC link stations generate some pretty unpleasantly rectangular current bursts and rely on other grid elements to spread what are in effect  current impulses more uniformly across the cycle. In the hopelessly simplified circuit below the upper wave-forms near the in and out terminals illustrate this. (The pale grey sine is voltage and the darker bumpy thing represents the general form of the current into or out of the grid) 

    Instructions always say that a low impedance grid is needed to keep the voltage waveform from becoming more like that of the current. (sometimes expressed as harmonic content vs supply impedance)
    Removing e.g. the French AC connection and leaving a large DC station on would perhaps  have been problematic in this way
    M

Children
  • This is the E&T magazine's summary of the report.    E&T magazine Iberian blackout

    David

  • I note that mentions reactive power as well - but the authors have put it in quotes, as if thay are not sure if imaginary currents are quite as real as real ones ;-)

    Hehe.

    I've always thought that calling things phase shifted to be orthogonal relative to 'reality' 'imaginary' a very misleading choice of naming convention. Thanks maths department.  However, I'm not sure that the engineering folk calling it 'reactive' power is much better. Perhaps the metalanguage we use needs a bit of a rethink. 'Early and late' currents or 'tidal circulation' might be clearer. We need to imply the sort of rolling pay day loan of electrons with a lot of effort but nothing useful being done.
    Mike