No neutral in Panel board for 3phase pumps that do not require a neutral

Hi all, on a recent EICR I have discovered a Panel board with no neutral but it is labelled for 3phase pumps only that do not require a neutral what are your thoughts on this matter? 

Parents
  • On the face of it I don't see a problem. In general there's no need to run a N conductor if there's nothing to connect it to - that's why they manufacture 3-core (brown/black/grey) +c.p.c. cables.

       - Andy.

Reply
  • On the face of it I don't see a problem. In general there's no need to run a N conductor if there's nothing to connect it to - that's why they manufacture 3-core (brown/black/grey) +c.p.c. cables.

       - Andy.