Hi all.
Can anyone provide me with minimum permitted insulation resistance values for the following voltages and the standard (if any0 that references these values ?
3.3and 11kV
Many thanks
Hi all.
Can anyone provide me with minimum permitted insulation resistance values for the following voltages and the standard (if any0 that references these values ?
3.3and 11kV
Many thanks
On what? a transformer? A single insulator., dry prior to installation?
an overhead line of several km, exposed to wind and rain, same again in a coastal location? All 3 will be wildly different .
A transformer bare and brand new should be some few hundreds of megohms but core grounding methods and internal components such as switches, fuses, and taps may lower the results of insulation resistance tests.
A bare bush or insulator will be gigohms dry and brand new. Covered in salt spray and struggling, a lot less !!
Brand new paper or XPLE Cables are normally charged to a DC comparable to the peak AC and the leakage current monitored for some minutes. There will be some dielectric absorption, but current should settle to well less than 1mA per km. Once in service, it can get a lot worse before things need to be replaced.
DNOs usually have their in-house standards example https://www.spenergynetworks.co.uk/userfiles/file/SUB-02-613.pdf
Mike.
On what? a transformer? A single insulator., dry prior to installation?
an overhead line of several km, exposed to wind and rain, same again in a coastal location? All 3 will be wildly different .
A transformer bare and brand new should be some few hundreds of megohms but core grounding methods and internal components such as switches, fuses, and taps may lower the results of insulation resistance tests.
A bare bush or insulator will be gigohms dry and brand new. Covered in salt spray and struggling, a lot less !!
Brand new paper or XPLE Cables are normally charged to a DC comparable to the peak AC and the leakage current monitored for some minutes. There will be some dielectric absorption, but current should settle to well less than 1mA per km. Once in service, it can get a lot worse before things need to be replaced.
DNOs usually have their in-house standards example https://www.spenergynetworks.co.uk/userfiles/file/SUB-02-613.pdf
Mike.