Maximum permitted Insulation Resistance values HV

Hi all.

Can anyone provide me with minimum permitted insulation resistance values for the following voltages and the standard (if any0 that references these values ?

3.3and 11kV

Many thanks

Parents
  • There isn’t a single minimum IR for HV use the OEM limits and judge by temperature corrected readings and trend. As a rule of thumb, clean or dry new gear at 3.3 kV or 11 kV should be up in the GΩ range; readings down in the low hundreds of MΩ merit a closer look. For motors, follow IEEE 43 modern form wound: ≥100 MΩ at 40 C; random wound: kV + 1 MΩ). If OEM data is missing, the NETA tables are a practical guide.
Reply
  • There isn’t a single minimum IR for HV use the OEM limits and judge by temperature corrected readings and trend. As a rule of thumb, clean or dry new gear at 3.3 kV or 11 kV should be up in the GΩ range; readings down in the low hundreds of MΩ merit a closer look. For motors, follow IEEE 43 modern form wound: ≥100 MΩ at 40 C; random wound: kV + 1 MΩ). If OEM data is missing, the NETA tables are a practical guide.