I am installing cables for circuits, some of which are > than 700mts for roadside systems.
Protection has been a challenge and many cables have been massively oversized for all, or part, of their length.
One particular cable run is protected by a 40A MCB. The first 400mts are in 120mm2 SWA up to a splitter switch.
From the splitter switch it continues for a further 250mts in 35mm2 SWA.
Trimble passes the circuit.
But, the discussion point is the cable size reduction. I think it falls within 433.1.1, protection for all conductors within a circuit, and a fellow designer feels that it requires further protection as per 434.2.1 as it continues in a smaller CSA.
The protection has been sized as if the cable is 35mm2 for its full length, but the Zs would have fallen outside of the limits of the tripping times.
My understanding of 434.2.1 - conductor size reduction, is that it allows a short run of cable to be used on a protection size larger than the cable would normally be protected by, hence the 3mtr limitation on length, and doesn't apply to this type of circuit.
Discrimination for any further protection device will be almost impossible to add as it already has a number of levels of protection.
Any thoughts please?