Trimble Pro Design - Energy Let Through & Adiabatic Issues
Hi All
I’ve been in the industry for about 20 years but only just started to do some small designs on Trimble Pro Design Software. So far on the last hand full of projects been relatively problem free but on this particular project I’ve been having issues the prospective fault current. A direct measurement on site has been done as Ze 0.04 (5.8kA). The first issue I had is we are planning to fit Hager combined AFDD/RCBO which are rate at 6kA. As these will be protected by a Hager 200A MCCB its allows me to use back up protection which has now cleared the error. But the issue i have now is the Line & Earth Adiabatic equation is now throwing up errors on all my circuits. I believe the software’s may be think my 16A circuit with 2.5mm T&E is relying on solely the 200A for short circuit protection? On some it’s saying my CPC needs to be at least 13.5mm. I have tried everything I can to think of but with no luck. Can anyone shed some light on this, in particular if you use the software yourself. Thanks in advanced.
  • i don't know the software, so just guessing... one thought -  how long are the circuits? In the lack of anything obvious I wondering if there's something odd like Zs at the far end is too high for "instantaneous" operation of the MCB element of the RCBO and so it's thinking of much extended disconnection times - which might account for wanting a lager c.p.c. (either for adiabatic or lowering Zs). The theory doesn't entirely add up (it's ignoring the RCD element of the RCBO, but many prefer not to rely on RCDs for ADS if they can help it so there may be an option in the software to that effect?) and if the c.p.c. had to be 13.5mm² to meet the adiabatic then the line conductor would need to as well - so perhaps hinting it's an overall Zs rather than c.s.a. issue.  (Assuming a fault current of around 6kA and k=115 then 13.5mm² might suggest a disconnection time somewhere around 0.07s - far too slow for an MCB in instantaneous mode)
  • Hi Andy
    Thank you for taking the time to reply. I should have mentioned originally but I was trying to somewhat keep the original post a bit shorter but well as the CPC being too small it was also saying this about the line conductor as well. As the Ze (or Zs at the incoming supply in this case) is only 0.04 and some of these circuits are only 15 - 30m long I highly doubt it’s an issue with the Zs. Also, the software does have a different type of error that displays for high Zs as I’ve had to deal with that issue in the past. I believe it’s a case of a software issue rather than how the circuits have been set up. I’m trying to use the Hager 200A MCCB to back up the breaking capacity of the Hager 6kA AFDD/RCBO but obviously still want the AFDD/RCBO to still protect the circuit on short circuit & overload.
  • Hello, the easiest thing to see what’s wrong is to generate a report from the software which should tell you what fault current and disconnection time it is considering for adiabatic check for earth fault and let through energy for phase fault - Note you can generate report even if there are errors. If it considers the disconnection time corresponding to 200A MCCB which you can easily verify from generating the TCC curve from software and checking the disconnection time w.r.to propspective fault current, then you are correct in your assumption. However, it shouldn’t do that and there must be a way around it - if you can send an email to Trimble support with your model and question, they should help. If you don’t have support care package it’s unlikely they will entertain such question in which case let me know and I will have a look at your model. Thanks.
  • Hi, to help with the issue you are experiencing with Trimble Prodesign software, you may be required to provide more information to get the issue resolved.
    However, a quick look at the brief information provided, a manual fault calculation for a Ze of 0.04Ohms, 5.8kA will be an estimated fault current for a single phase circuit but the fault current of a 3phase is at about 10kA.
    I am not too conversant with Hagger's product but my quick check of your issue shows that the Hagger's 200A MCCB cannot provide more than 10kA back up protection for Harger's 16A AFDD/RCBO device and the software's Pscc is is at 15.3kA.
    To get things resolved, I would advice you check Hagger's selectivity tables for back-up protection to see the range of options to explore.