Trimble Pro Design - Energy Let Through & Adiabatic Issues

Hi All

I’ve been in the industry for about 20 years but only just started to do some small designs on Trimble Pro Design Software. So far on the last hand full of projects been relatively problem free but on this particular project I’ve been having issues the prospective fault current. A direct measurement on site has been done as Ze 0.04 (5.8kA). The first issue I had is we are planning to fit Hager combined AFDD/RCBO which are rate at 6kA. As these will be protected by a Hager 200A MCCB its allows me to use back up protection which has now cleared the error. But the issue i have now is the Line & Earth Adiabatic equation is now throwing up errors on all my circuits. I believe the software’s may be think my 16A circuit with 2.5mm T&E is relying on solely the 200A for short circuit protection? On some it’s saying my CPC needs to be at least 13.5mm. I have tried everything I can to think of but with no luck. Can anyone shed some light on this, in particular if you use the software yourself. Thanks in advanced.

Parents
  • Hello, the easiest thing to see what’s wrong is to generate a report from the software which should tell you what fault current and disconnection time it is considering for adiabatic check for earth fault and let through energy for phase fault - Note you can generate report even if there are errors. If it considers the disconnection time corresponding to 200A MCCB which you can easily verify from generating the TCC curve from software and checking the disconnection time w.r.to propspective fault current, then you are correct in your assumption. However, it shouldn’t do that and there must be a way around it - if you can send an email to Trimble support with your model and question, they should help. If you don’t have support care package it’s unlikely they will entertain such question in which case let me know and I will have a look at your model. Thanks. 

Reply
  • Hello, the easiest thing to see what’s wrong is to generate a report from the software which should tell you what fault current and disconnection time it is considering for adiabatic check for earth fault and let through energy for phase fault - Note you can generate report even if there are errors. If it considers the disconnection time corresponding to 200A MCCB which you can easily verify from generating the TCC curve from software and checking the disconnection time w.r.to propspective fault current, then you are correct in your assumption. However, it shouldn’t do that and there must be a way around it - if you can send an email to Trimble support with your model and question, they should help. If you don’t have support care package it’s unlikely they will entertain such question in which case let me know and I will have a look at your model. Thanks. 

Children
No Data