Legh Richardson:
I would have thought a generic pump motor would have a start up current up to 8 times the full load current. On the surface it may not trip as its below the instantaneous tripping current rating of the MCB. However, I have seen 2 times 300W lighting transformers take out C6 breakers. So perhaps I'd rate the MCB for this particular job at C6.
Legh Richardson:
I would have thought a generic pump motor would have a start up current up to 8 times the full load current. On the surface it may not trip as its below the instantaneous tripping current rating of the MCB. However, I have seen 2 times 300W lighting transformers take out C6 breakers. So perhaps I'd rate the MCB for this particular job at C6.