Legh Richardson:
Here's a R1+R2 table used to calculate the earth loop impedance using SWA armour for R2, (Zs), You can then calculate the prospective short circuit current and hence the adiabatic calculation.
Legh
Zoomup:
Without doing any calculations and just using previous "experience knowledge" I venture to say that the proposed installation as described will comply.
But I may be concerned about Volt drop. What is the design load and installation method?
Z.
Stewart Mason:
With what Graham has said I'm slightly confused.
So with a Ze of 0.35, a 16A 60898 type B, and 30 metres of 2c 2.5mm using the SWA as the earth would this comply?
Thank you.
°Zoomup:
Zoomup:
Without doing any calculations and just using previous "experience knowledge" I venture to say that the proposed installation as described will comply.
But I may be concerned about Volt drop. What is the design load and installation method?
Z.CORRECTION. Now, after doing some quick sums I now believe that the disconnection time will be nearer to 10 seconds with an earth fault of negligible impedance at the far end of the S.W.A. That just shows us what guessing can achieve.......bad results. The C.P.C. needs to be bigger, supplemented with an additional copper C.P.C. or an R.C.D. installed at the origin of the circuit.
Z.