Without doing any calculations and just using previous "experience knowledge" I venture to say that the proposed installation as described will comply.
But I may be concerned about Volt drop. What is the design load and installation method?
Z.CORRECTION. Now, after doing some quick sums I now believe that the disconnection time will be nearer to 10 seconds with an earth fault of negligible impedance at the far end of the S.W.A. That just shows us what guessing can achieve.......bad results. The C.P.C. needs to be bigger, supplemented with an additional copper C.P.C. or an R.C.D. installed at the origin of the circuit.
Z.
°Zoomup:
Zoomup:
Without doing any calculations and just using previous "experience knowledge" I venture to say that the proposed installation as described will comply.
But I may be concerned about Volt drop. What is the design load and installation method?
Z.CORRECTION. Now, after doing some quick sums I now believe that the disconnection time will be nearer to 10 seconds with an earth fault of negligible impedance at the far end of the S.W.A. That just shows us what guessing can achieve.......bad results. The C.P.C. needs to be bigger, supplemented with an additional copper C.P.C. or an R.C.D. installed at the origin of the circuit.