gkenyon:
Nope.
What are you getting at?
This particular example hasn't been stated as low fault level, so we must assume 16 kA (and 0.35 omega Ze) - of course could be higher fault level if larger supply than the standard 100 A.
As I stated, it's not the fault level at the end of the cable that's important, it's the fault level at the start of the cable.
However, no para in EIDG still says the same thing.
I'm sure someone will point out that "in many houses the fault level is below 3 kA" - well, it's not in mine, which is often over 6 kA, and I'm over half way down our street from the substation.
gkenyon:
Nope.
What are you getting at?
This particular example hasn't been stated as low fault level, so we must assume 16 kA (and 0.35 omega Ze) - of course could be higher fault level if larger supply than the standard 100 A.
As I stated, it's not the fault level at the end of the cable that's important, it's the fault level at the start of the cable.
However, no para in EIDG still says the same thing.
I'm sure someone will point out that "in many houses the fault level is below 3 kA" - well, it's not in mine, which is often over 6 kA, and I'm over half way down our street from the substation.